ᐅ Hydraulic balancing for air-to-water heat pump + high-efficiency circulation pump

Created on: 3 Jan 2021 23:07
L
lesmue79
Warning: wall of text and lots of theorycrafting:

I am currently trying to optimize or fundamentally adjust the hydraulic and thermal balancing of my air-to-water heat pump system, including underfloor heating, but I am running into the following issues:

First, about the house: KfW-55 bungalow with controlled mechanical ventilation
Nearly 105 m2 (1130 ft²) of heated floor area
Air-to-water heat pump with underfloor heating throughout, 10cm (5 inches) pipe spacing, max 30°C (86°F) flow temperature. At -12°C (10°F) outside temperature, the calculated heating load is 3276 watts.

According to the datasheet, the heat pump delivers 3200 watts at -10°C (14°F) outside temperature with flow 35°C (95°F) and return 30°C (86°F).

All rooms are designed for 20°C (68°F), including the bathroom (to avoid an oversized heat pump by the general contractor). Additionally, for the bathroom, an electric radiator is planned to achieve a room temperature of 2°C (4°F) higher than the rest. However, in reality, the toilet, utility room, bedroom, and guest room should only be heated to 18°C (64°F) (it won’t be much lower in a new building). The bathroom is intended to be warmer, at around 21–22°C (70–72°F).

Currently, I have the following questions (though perhaps I am too focused on the self-regulation effect and avoiding actuator valves):

1. Circulation pump: Various guides, manuals, and forum posts recommend setting the circulation pump of the underfloor heating to a constant flow rate.

My conclusion: my circulation pump is a high-efficiency variable-speed pump, so I can set the flow rate on the manifold in L/min (based on the calculations from the general contractor / heating engineer) to whatever I want, but the flow always settles around 600–630 L/h (10–11 L/min). The only significant flow changes I get are when I activate the actuators and room thermostats, which then open or close the valves. The only adjustment parameter on the circulation pump is the minimum flow rate; no other settings are available. But I don’t fully understand how this function works.

2. Operating times of the heat pump / self-regulation: I usually read that the heat pump should run as long as possible, though some sources say short cycling a few times is normal.

My conclusion: if I run the system without actuators and room thermostats, the energy integral control does not work; the system basically runs almost 24/7 at low temperatures, with interruptions only for defrosting. As a result, with a flow temperature of 27°C (81°F), I only get about 19–20°C (66–68°F) room temperature, but I’d prefer around 21–23°C (70–73°F), especially in the bathroom. If I do it the other way, with energy integral control (EIC) and actuators and slightly higher curve so that 30°C (86°F) flow is demanded, the actuators close in the first rooms, which causes the flow to increase to the other rooms because the pump still distributes the volume flow among the remaining open valves. At the same time, the flow temperature rises for rooms where the actuators are still open until the desired temperature is reached and the actuators close. Then the energy integral kicks in and goes negative because actual flow temperature exceeds setpoint flow temperature, until the heat pump shuts off once the energy integral has been reduced.

So right now, I’m struggling with what is better: should the system just run steadily at a flow temperature of 27°C (81°F) (which I might still optimize a bit), with heating only interrupted for defrosting or when the compressor’s hysteresis is exceeded, causing the compressor to be locked out for a certain time? Or should I define time windows during which the system is allowed to operate?

Maybe I could manage this better by refining the balancing, but I guess I’ll have to throttle down so much for the energy integral to work that the flow rate will fall below the minimum required, and the bypass valve will open.

Or should I run the system at 30°C (86°F) flow with room thermostats and actuators, allowing the energy integral control to function properly and reach the desired room temperatures?

Another strange issue is: according to the heating load and underfloor heating calculations, the system requires about 840 L/h (14 L/min) at 4.4 K (7.9°F) delta T in the design case. If I set the flow according to this calculation or slightly lower, the pump only delivers 600–630 L/h (10–11 L/min) at a delta T of about 3–4 K (5.4–7.2°F).

According to the datasheet, the optimal flow rate for the heat pump is 540 L/h (9 L/min) at 5 K (9°F) delta T.

540 L/h * 5 K * 1.163 = 3132 watts
620 L/h * 3.5 K * 1.163 = 2527 watts
840 L/h * 4.4 K * 1.163 = 4287 watts
Calculated heating load at -12°C (10°F) = 3176 watts (and this heating load is probably overestimated since controlled mechanical ventilation was not included in the calculation, and I want only 15–18°C (59–64°F) in four rooms instead of the calculated 20°C (68°F). Also, average outside temperatures for the heat pump in my area are closer to -10°C (14°F) rather than -12°C (10°F), so there is some margin).

Maybe I have now gotten too caught up in theoretical and calculated values and can’t see the forest for the trees?
B
Bookstar
6 Jan 2021 21:04
We currently have about 26 kWh of heating energy at an average temperature of -1°C (30°F) for 210 m² (2,260 sq ft) of heated area. This is just a reference for you. In my opinion, you should aim for around 15 kWh per day.
L
lesmue79
6 Jan 2021 21:26
Bookstar schrieb:

Currently, with an average temperature of -1 degree Celsius (30°F), we use about 26 kWh of heating energy for 210 m² (2260 sq ft) of heated area. Just as a reference for you. In my opinion, you should be somewhere around 15 kWh per day.

What average room temperature do you maintain? And what heating system do you use—also a air-to-water heat pump?
B
Bookstar
6 Jan 2021 21:31
Yes, even with an air-to-water heat pump, we have 22 degrees Celsius (72°F) in the living areas and 19 degrees Celsius (66°F) in the bedrooms.
L
lesmue79
7 Jan 2021 19:41
Temperatures today are more or less the same as the day before, so I have now lowered the heating curve from 0.25 to 0.20.

What honestly still bothers me is how the system controls and the circulation pump with its variable flow rate.

Normally, when throttling individual heating circuits, the flow rate should redistribute to the remaining open circuits, right?

If I now reduce the flow rate in the WC and utility room to 0.5 liters (0.13 gallons) for testing purposes, down from the original 1.5 and 1.0 liters per minute (0.4 and 0.26 gallons per minute), the total system flow rate also decreases. But this means that the throttled flow rate is not available anywhere else in the system; the pump just pushes less?
T
T_im_Norden
7 Jan 2021 19:48
I assume this is due to the pump control system, which adjusts itself.

I would put that aside for now and first see how much the balancing helps.

If you can achieve good values with that, there is no need to worry too much about the flow rate.
L
lesmue79
7 Jan 2021 20:02
It’s just a thought that’s been on my mind: I will, of course, continue lowering the heating curve.

Once I have the heating curve set low, I can activate the actuators for one or two days as a test... But I will do that before restricting anything...