ᐅ Hydraulic balancing for air-to-water heat pump + high-efficiency circulation pump

Created on: 3 Jan 2021 23:07
L
lesmue79
Warning: wall of text and lots of theorycrafting:

I am currently trying to optimize or fundamentally adjust the hydraulic and thermal balancing of my air-to-water heat pump system, including underfloor heating, but I am running into the following issues:

First, about the house: KfW-55 bungalow with controlled mechanical ventilation
Nearly 105 m2 (1130 ft²) of heated floor area
Air-to-water heat pump with underfloor heating throughout, 10cm (5 inches) pipe spacing, max 30°C (86°F) flow temperature. At -12°C (10°F) outside temperature, the calculated heating load is 3276 watts.

According to the datasheet, the heat pump delivers 3200 watts at -10°C (14°F) outside temperature with flow 35°C (95°F) and return 30°C (86°F).

All rooms are designed for 20°C (68°F), including the bathroom (to avoid an oversized heat pump by the general contractor). Additionally, for the bathroom, an electric radiator is planned to achieve a room temperature of 2°C (4°F) higher than the rest. However, in reality, the toilet, utility room, bedroom, and guest room should only be heated to 18°C (64°F) (it won’t be much lower in a new building). The bathroom is intended to be warmer, at around 21–22°C (70–72°F).

Currently, I have the following questions (though perhaps I am too focused on the self-regulation effect and avoiding actuator valves):

1. Circulation pump: Various guides, manuals, and forum posts recommend setting the circulation pump of the underfloor heating to a constant flow rate.

My conclusion: my circulation pump is a high-efficiency variable-speed pump, so I can set the flow rate on the manifold in L/min (based on the calculations from the general contractor / heating engineer) to whatever I want, but the flow always settles around 600–630 L/h (10–11 L/min). The only significant flow changes I get are when I activate the actuators and room thermostats, which then open or close the valves. The only adjustment parameter on the circulation pump is the minimum flow rate; no other settings are available. But I don’t fully understand how this function works.

2. Operating times of the heat pump / self-regulation: I usually read that the heat pump should run as long as possible, though some sources say short cycling a few times is normal.

My conclusion: if I run the system without actuators and room thermostats, the energy integral control does not work; the system basically runs almost 24/7 at low temperatures, with interruptions only for defrosting. As a result, with a flow temperature of 27°C (81°F), I only get about 19–20°C (66–68°F) room temperature, but I’d prefer around 21–23°C (70–73°F), especially in the bathroom. If I do it the other way, with energy integral control (EIC) and actuators and slightly higher curve so that 30°C (86°F) flow is demanded, the actuators close in the first rooms, which causes the flow to increase to the other rooms because the pump still distributes the volume flow among the remaining open valves. At the same time, the flow temperature rises for rooms where the actuators are still open until the desired temperature is reached and the actuators close. Then the energy integral kicks in and goes negative because actual flow temperature exceeds setpoint flow temperature, until the heat pump shuts off once the energy integral has been reduced.

So right now, I’m struggling with what is better: should the system just run steadily at a flow temperature of 27°C (81°F) (which I might still optimize a bit), with heating only interrupted for defrosting or when the compressor’s hysteresis is exceeded, causing the compressor to be locked out for a certain time? Or should I define time windows during which the system is allowed to operate?

Maybe I could manage this better by refining the balancing, but I guess I’ll have to throttle down so much for the energy integral to work that the flow rate will fall below the minimum required, and the bypass valve will open.

Or should I run the system at 30°C (86°F) flow with room thermostats and actuators, allowing the energy integral control to function properly and reach the desired room temperatures?

Another strange issue is: according to the heating load and underfloor heating calculations, the system requires about 840 L/h (14 L/min) at 4.4 K (7.9°F) delta T in the design case. If I set the flow according to this calculation or slightly lower, the pump only delivers 600–630 L/h (10–11 L/min) at a delta T of about 3–4 K (5.4–7.2°F).

According to the datasheet, the optimal flow rate for the heat pump is 540 L/h (9 L/min) at 5 K (9°F) delta T.

540 L/h * 5 K * 1.163 = 3132 watts
620 L/h * 3.5 K * 1.163 = 2527 watts
840 L/h * 4.4 K * 1.163 = 4287 watts
Calculated heating load at -12°C (10°F) = 3176 watts (and this heating load is probably overestimated since controlled mechanical ventilation was not included in the calculation, and I want only 15–18°C (59–64°F) in four rooms instead of the calculated 20°C (68°F). Also, average outside temperatures for the heat pump in my area are closer to -10°C (14°F) rather than -12°C (10°F), so there is some margin).

Maybe I have now gotten too caught up in theoretical and calculated values and can’t see the forest for the trees?
H
Hausbau 55
27 Dec 2021 19:06
lesmue79 schrieb:

A brief update:

By now, I have figured out the heating curve and temperature adjustments for us and our house:

Heating curve 0.10 with a base point increase of 1°C (1.8°F).

In all main rooms, the temperature is 20.5 or 21°C (69°F or 70°F) as desired.

Electricity consumption from yesterday morning to today morning at 1°C (34°F) outdoor temperature was 12 kWh for heating and 2 kWh for hot water.

The compressor essentially runs almost 24 hours a day.


Hello lesmue79,

I have reread your approach regarding the hydraulic balancing. I am very interested in this topic since I am also getting a heat pump from Vaillant, not a split system but the Arotherm Plus 35/6. Many parameters of our heat pumps are quite similar.

Now I would like to hear your conclusion after using it for a full year. Please share information about consumption, energy use, and electricity – the more detailed, the better.

Thank you in advance! Unfortunately, I have been waiting for several weeks for the installation of my heat pump. Vaillant seems to be unable to deliver. As a result, we had to heat our screed using a hot-air blower. In total, over 2200 kWh for a 90 m² (970 ft²) bungalow. Not ideal at all.
Tolentino27 Dec 2021 19:16
That’s still manageable; I am now almost at 4500 kW. However, lately, I am only using fan heaters and infrared panels...
Apparently, I am even directly on a priority list at Vaillant...
L
lesmue79
27 Dec 2021 20:02
Hausbau 55 schrieb:

Hello lesmue79,

I have reread your process for the hydraulic balancing. I am very interested in this topic since I am also getting a heat pump from Vaillant—not a split unit, but the Arotherm Plus 35/6. Many of the parameters of our heat pumps are similar.
Now I would like to hear your conclusion after a full year of use. Please also provide information on energy and electricity consumption. The more detailed, the better...
Thanks in advance!
Unfortunately, I have been waiting for several weeks for the installation of my heat pump. Vaillant apparently cannot deliver at the moment. As a result, we had to use a heat gun (Hotboy) to dry our screed. In total, over 2200 kWh for a 90 m² (970 sq ft) bungalow. Definitely not ideal.

I will write something about this but need to use my laptop—I can’t type on my phone from the couch in the evening because the topic is too extensive.
H
Hausbau 55
27 Dec 2021 20:28
Tolentino schrieb:

That’s still manageable; I’m currently at almost 4500 kW. However, by now I’m only using electric fan heaters and infrared panels...
Apparently, I’m even on a priority list directly with Vaillant...

Besides the Hotboy, there were also 2 construction dryers running. The very high screed temperatures were at least ideal for construction drying.
Which Vaillant heat pump are you getting? My heat pump was ordered by the heating contractor from the wholesaler at the end of September. At the beginning of the new year, I will also inquire more closely about a delivery date. We could actually move in by the end of January...
H
Hausbau 55
27 Dec 2021 20:31
lesmue79 schrieb:

I will write something about it, but I need to use my laptop for that since typing on my phone on the couch in the evening makes the topic too extensive.
Sounds good. Your experiences after the recent subzero temperatures are certainly insightful. How low did the temperatures drop, and what is the natural air temperature (NAT) in your area? Did you have your flow temperature below 30°C (86°F)?
Tolentino27 Dec 2021 21:06
The VWL 75/6 is therefore two sizes larger than yours. Actually, the 55 would have been sufficient, but it was not eligible for funding and also did not have enough pump capacity.