ᐅ Hydraulic balancing for air-to-water heat pump + high-efficiency circulation pump

Created on: 3 Jan 2021 23:07
L
lesmue79
L
lesmue79
3 Jan 2021 23:07
Warning: wall of text and lots of theorycrafting:

I am currently trying to optimize or fundamentally adjust the hydraulic and thermal balancing of my air-to-water heat pump system, including underfloor heating, but I am running into the following issues:

First, about the house: KfW-55 bungalow with controlled mechanical ventilation
Nearly 105 m2 (1130 ft²) of heated floor area
Air-to-water heat pump with underfloor heating throughout, 10cm (5 inches) pipe spacing, max 30°C (86°F) flow temperature. At -12°C (10°F) outside temperature, the calculated heating load is 3276 watts.

According to the datasheet, the heat pump delivers 3200 watts at -10°C (14°F) outside temperature with flow 35°C (95°F) and return 30°C (86°F).

All rooms are designed for 20°C (68°F), including the bathroom (to avoid an oversized heat pump by the general contractor). Additionally, for the bathroom, an electric radiator is planned to achieve a room temperature of 2°C (4°F) higher than the rest. However, in reality, the toilet, utility room, bedroom, and guest room should only be heated to 18°C (64°F) (it won’t be much lower in a new building). The bathroom is intended to be warmer, at around 21–22°C (70–72°F).

Currently, I have the following questions (though perhaps I am too focused on the self-regulation effect and avoiding actuator valves):

1. Circulation pump: Various guides, manuals, and forum posts recommend setting the circulation pump of the underfloor heating to a constant flow rate.

My conclusion: my circulation pump is a high-efficiency variable-speed pump, so I can set the flow rate on the manifold in L/min (based on the calculations from the general contractor / heating engineer) to whatever I want, but the flow always settles around 600–630 L/h (10–11 L/min). The only significant flow changes I get are when I activate the actuators and room thermostats, which then open or close the valves. The only adjustment parameter on the circulation pump is the minimum flow rate; no other settings are available. But I don’t fully understand how this function works.

2. Operating times of the heat pump / self-regulation: I usually read that the heat pump should run as long as possible, though some sources say short cycling a few times is normal.

My conclusion: if I run the system without actuators and room thermostats, the energy integral control does not work; the system basically runs almost 24/7 at low temperatures, with interruptions only for defrosting. As a result, with a flow temperature of 27°C (81°F), I only get about 19–20°C (66–68°F) room temperature, but I’d prefer around 21–23°C (70–73°F), especially in the bathroom. If I do it the other way, with energy integral control (EIC) and actuators and slightly higher curve so that 30°C (86°F) flow is demanded, the actuators close in the first rooms, which causes the flow to increase to the other rooms because the pump still distributes the volume flow among the remaining open valves. At the same time, the flow temperature rises for rooms where the actuators are still open until the desired temperature is reached and the actuators close. Then the energy integral kicks in and goes negative because actual flow temperature exceeds setpoint flow temperature, until the heat pump shuts off once the energy integral has been reduced.

So right now, I’m struggling with what is better: should the system just run steadily at a flow temperature of 27°C (81°F) (which I might still optimize a bit), with heating only interrupted for defrosting or when the compressor’s hysteresis is exceeded, causing the compressor to be locked out for a certain time? Or should I define time windows during which the system is allowed to operate?

Maybe I could manage this better by refining the balancing, but I guess I’ll have to throttle down so much for the energy integral to work that the flow rate will fall below the minimum required, and the bypass valve will open.

Or should I run the system at 30°C (86°F) flow with room thermostats and actuators, allowing the energy integral control to function properly and reach the desired room temperatures?

Another strange issue is: according to the heating load and underfloor heating calculations, the system requires about 840 L/h (14 L/min) at 4.4 K (7.9°F) delta T in the design case. If I set the flow according to this calculation or slightly lower, the pump only delivers 600–630 L/h (10–11 L/min) at a delta T of about 3–4 K (5.4–7.2°F).

According to the datasheet, the optimal flow rate for the heat pump is 540 L/h (9 L/min) at 5 K (9°F) delta T.

540 L/h * 5 K * 1.163 = 3132 watts
620 L/h * 3.5 K * 1.163 = 2527 watts
840 L/h * 4.4 K * 1.163 = 4287 watts
Calculated heating load at -12°C (10°F) = 3176 watts (and this heating load is probably overestimated since controlled mechanical ventilation was not included in the calculation, and I want only 15–18°C (59–64°F) in four rooms instead of the calculated 20°C (68°F). Also, average outside temperatures for the heat pump in my area are closer to -10°C (14°F) rather than -12°C (10°F), so there is some margin).

Maybe I have now gotten too caught up in theoretical and calculated values and can’t see the forest for the trees?
D
Daniel-Sp
3 Jan 2021 23:23
What kind of heat pump do you actually have?
T
T_im_Norden
4 Jan 2021 06:52
On which manifold do you want to set the flow rate?

Many pumps have the option to switch to constant flow rate either through the control unit or directly on the device.

Theory is what has been calculated; practice is what you can achieve in your specific situation. So it is quite possible that the 27°C (81°F) supply temperature is necessary.

Are you able to reach 19/20°C (66/68°F) room temperature in all rooms when all valves are fully open?
L
lesmue79
4 Jan 2021 08:09
It is the smallest new Arotherm Split from Vaillant, with a heating capacity of about 3.x kW.

I can limit the flow rates at the heating circuit distributor either by adjusting the return flow or by setting the Tacosetter/flow meter on the supply line.

Regarding the pump, I can only adjust the residual head from 200 mbar to 900 mbar, with Vaillant stating that 900 mbar corresponds to 100% pump power. I even checked inside the device at the pump to see if there might be a control screw to adjust the settings or steps, but there is none.

I achieve 19°C/20°C (66°F/68°F) throughout the house, even in rooms where I actually want a lower room temperature. In other words, it has never been too cold for us since we moved in.
L
lesmue79
4 Jan 2021 08:13
Technical datasheet with electrical and refrigerant circuit data for VWL models.

Table with water quality, pressure, and temperature values for VWL 58/5 IS vs. VWL 78/5 IS
T
T_im_Norden
4 Jan 2021 08:28
Are all the heating circuits fully open at 19°C (66°F) or 20°C (68°F)?

If not:
Record all settings and then
completely disable all heating circuits.
Monitor the temperatures.

If yes:
Record all settings and then
reduce the flow rate for the first room that should be cooler.
Wait at least 24 hours and observe the temperature.

Repeat this until the room temperature is suitable.

Note: Changes can take significantly longer than 24 hours to take effect.
With a supply temperature of 27°C (81°F) or less, it may take several days to stabilize.

It is likely that adjusting the flow in this room will also affect the temperatures in other rooms, so monitor those as well.

In principle, it is acceptable for the heat pump to run continuously.

The integral function essentially means that the current supply temperature exceeds the calculated target supply temperature, and the system will stop heating until the target supply temperature is reached again.