ᐅ Hydraulic balancing for air-to-water heat pump + high-efficiency circulation pump
Created on: 3 Jan 2021 23:07
L
lesmue79
Warning: wall of text and lots of theorycrafting:
I am currently trying to optimize or fundamentally adjust the hydraulic and thermal balancing of my air-to-water heat pump system, including underfloor heating, but I am running into the following issues:
First, about the house: KfW-55 bungalow with controlled mechanical ventilation
Nearly 105 m2 (1130 ft²) of heated floor area
Air-to-water heat pump with underfloor heating throughout, 10cm (5 inches) pipe spacing, max 30°C (86°F) flow temperature. At -12°C (10°F) outside temperature, the calculated heating load is 3276 watts.
According to the datasheet, the heat pump delivers 3200 watts at -10°C (14°F) outside temperature with flow 35°C (95°F) and return 30°C (86°F).
All rooms are designed for 20°C (68°F), including the bathroom (to avoid an oversized heat pump by the general contractor). Additionally, for the bathroom, an electric radiator is planned to achieve a room temperature of 2°C (4°F) higher than the rest. However, in reality, the toilet, utility room, bedroom, and guest room should only be heated to 18°C (64°F) (it won’t be much lower in a new building). The bathroom is intended to be warmer, at around 21–22°C (70–72°F).
Currently, I have the following questions (though perhaps I am too focused on the self-regulation effect and avoiding actuator valves):
1. Circulation pump: Various guides, manuals, and forum posts recommend setting the circulation pump of the underfloor heating to a constant flow rate.
My conclusion: my circulation pump is a high-efficiency variable-speed pump, so I can set the flow rate on the manifold in L/min (based on the calculations from the general contractor / heating engineer) to whatever I want, but the flow always settles around 600–630 L/h (10–11 L/min). The only significant flow changes I get are when I activate the actuators and room thermostats, which then open or close the valves. The only adjustment parameter on the circulation pump is the minimum flow rate; no other settings are available. But I don’t fully understand how this function works.
2. Operating times of the heat pump / self-regulation: I usually read that the heat pump should run as long as possible, though some sources say short cycling a few times is normal.
My conclusion: if I run the system without actuators and room thermostats, the energy integral control does not work; the system basically runs almost 24/7 at low temperatures, with interruptions only for defrosting. As a result, with a flow temperature of 27°C (81°F), I only get about 19–20°C (66–68°F) room temperature, but I’d prefer around 21–23°C (70–73°F), especially in the bathroom. If I do it the other way, with energy integral control (EIC) and actuators and slightly higher curve so that 30°C (86°F) flow is demanded, the actuators close in the first rooms, which causes the flow to increase to the other rooms because the pump still distributes the volume flow among the remaining open valves. At the same time, the flow temperature rises for rooms where the actuators are still open until the desired temperature is reached and the actuators close. Then the energy integral kicks in and goes negative because actual flow temperature exceeds setpoint flow temperature, until the heat pump shuts off once the energy integral has been reduced.
So right now, I’m struggling with what is better: should the system just run steadily at a flow temperature of 27°C (81°F) (which I might still optimize a bit), with heating only interrupted for defrosting or when the compressor’s hysteresis is exceeded, causing the compressor to be locked out for a certain time? Or should I define time windows during which the system is allowed to operate?
Maybe I could manage this better by refining the balancing, but I guess I’ll have to throttle down so much for the energy integral to work that the flow rate will fall below the minimum required, and the bypass valve will open.
Or should I run the system at 30°C (86°F) flow with room thermostats and actuators, allowing the energy integral control to function properly and reach the desired room temperatures?
Another strange issue is: according to the heating load and underfloor heating calculations, the system requires about 840 L/h (14 L/min) at 4.4 K (7.9°F) delta T in the design case. If I set the flow according to this calculation or slightly lower, the pump only delivers 600–630 L/h (10–11 L/min) at a delta T of about 3–4 K (5.4–7.2°F).
According to the datasheet, the optimal flow rate for the heat pump is 540 L/h (9 L/min) at 5 K (9°F) delta T.
540 L/h * 5 K * 1.163 = 3132 watts
620 L/h * 3.5 K * 1.163 = 2527 watts
840 L/h * 4.4 K * 1.163 = 4287 watts
Calculated heating load at -12°C (10°F) = 3176 watts (and this heating load is probably overestimated since controlled mechanical ventilation was not included in the calculation, and I want only 15–18°C (59–64°F) in four rooms instead of the calculated 20°C (68°F). Also, average outside temperatures for the heat pump in my area are closer to -10°C (14°F) rather than -12°C (10°F), so there is some margin).
Maybe I have now gotten too caught up in theoretical and calculated values and can’t see the forest for the trees?
I am currently trying to optimize or fundamentally adjust the hydraulic and thermal balancing of my air-to-water heat pump system, including underfloor heating, but I am running into the following issues:
First, about the house: KfW-55 bungalow with controlled mechanical ventilation
Nearly 105 m2 (1130 ft²) of heated floor area
Air-to-water heat pump with underfloor heating throughout, 10cm (5 inches) pipe spacing, max 30°C (86°F) flow temperature. At -12°C (10°F) outside temperature, the calculated heating load is 3276 watts.
According to the datasheet, the heat pump delivers 3200 watts at -10°C (14°F) outside temperature with flow 35°C (95°F) and return 30°C (86°F).
All rooms are designed for 20°C (68°F), including the bathroom (to avoid an oversized heat pump by the general contractor). Additionally, for the bathroom, an electric radiator is planned to achieve a room temperature of 2°C (4°F) higher than the rest. However, in reality, the toilet, utility room, bedroom, and guest room should only be heated to 18°C (64°F) (it won’t be much lower in a new building). The bathroom is intended to be warmer, at around 21–22°C (70–72°F).
Currently, I have the following questions (though perhaps I am too focused on the self-regulation effect and avoiding actuator valves):
1. Circulation pump: Various guides, manuals, and forum posts recommend setting the circulation pump of the underfloor heating to a constant flow rate.
My conclusion: my circulation pump is a high-efficiency variable-speed pump, so I can set the flow rate on the manifold in L/min (based on the calculations from the general contractor / heating engineer) to whatever I want, but the flow always settles around 600–630 L/h (10–11 L/min). The only significant flow changes I get are when I activate the actuators and room thermostats, which then open or close the valves. The only adjustment parameter on the circulation pump is the minimum flow rate; no other settings are available. But I don’t fully understand how this function works.
2. Operating times of the heat pump / self-regulation: I usually read that the heat pump should run as long as possible, though some sources say short cycling a few times is normal.
My conclusion: if I run the system without actuators and room thermostats, the energy integral control does not work; the system basically runs almost 24/7 at low temperatures, with interruptions only for defrosting. As a result, with a flow temperature of 27°C (81°F), I only get about 19–20°C (66–68°F) room temperature, but I’d prefer around 21–23°C (70–73°F), especially in the bathroom. If I do it the other way, with energy integral control (EIC) and actuators and slightly higher curve so that 30°C (86°F) flow is demanded, the actuators close in the first rooms, which causes the flow to increase to the other rooms because the pump still distributes the volume flow among the remaining open valves. At the same time, the flow temperature rises for rooms where the actuators are still open until the desired temperature is reached and the actuators close. Then the energy integral kicks in and goes negative because actual flow temperature exceeds setpoint flow temperature, until the heat pump shuts off once the energy integral has been reduced.
So right now, I’m struggling with what is better: should the system just run steadily at a flow temperature of 27°C (81°F) (which I might still optimize a bit), with heating only interrupted for defrosting or when the compressor’s hysteresis is exceeded, causing the compressor to be locked out for a certain time? Or should I define time windows during which the system is allowed to operate?
Maybe I could manage this better by refining the balancing, but I guess I’ll have to throttle down so much for the energy integral to work that the flow rate will fall below the minimum required, and the bypass valve will open.
Or should I run the system at 30°C (86°F) flow with room thermostats and actuators, allowing the energy integral control to function properly and reach the desired room temperatures?
Another strange issue is: according to the heating load and underfloor heating calculations, the system requires about 840 L/h (14 L/min) at 4.4 K (7.9°F) delta T in the design case. If I set the flow according to this calculation or slightly lower, the pump only delivers 600–630 L/h (10–11 L/min) at a delta T of about 3–4 K (5.4–7.2°F).
According to the datasheet, the optimal flow rate for the heat pump is 540 L/h (9 L/min) at 5 K (9°F) delta T.
540 L/h * 5 K * 1.163 = 3132 watts
620 L/h * 3.5 K * 1.163 = 2527 watts
840 L/h * 4.4 K * 1.163 = 4287 watts
Calculated heating load at -12°C (10°F) = 3176 watts (and this heating load is probably overestimated since controlled mechanical ventilation was not included in the calculation, and I want only 15–18°C (59–64°F) in four rooms instead of the calculated 20°C (68°F). Also, average outside temperatures for the heat pump in my area are closer to -10°C (14°F) rather than -12°C (10°F), so there is some margin).
Maybe I have now gotten too caught up in theoretical and calculated values and can’t see the forest for the trees?
T
T_im_Norden11 Jan 2021 12:40Let's see what Vaillant says. At 100% pump speed, the flow rate should be higher according to the diagram.
What still puzzles me is the statement that the system (according to the diagram) would operate optimally at a nominal flow rate of 540 l/h (1.42 US gallons per hour) and a 5 K temperature difference. I think I will test what happens if I throttle everything until the control shows 530 l/h (1.40 US gallons per hour) and whether the pump then regulates the flow rate at 5 K...
540 x 1.16 x 5 K = 3132 watts heating capacity
540 x 1.16 x 5 K = 3132 watts heating capacity
So, at 900 mbar, the temperature difference was 2°C (3.6°F) according to the regulation.
The same applied at the inlet of the heating circuit distributor.
For the individual heating circuits, it varied from 3°C (5.4°F) in the throttled circuits to 1.5°C (2.7°F).
I have now adjusted the pump from 900 mbar to 450 mbar.
The same applied at the inlet of the heating circuit distributor.
For the individual heating circuits, it varied from 3°C (5.4°F) in the throttled circuits to 1.5°C (2.7°F).
I have now adjusted the pump from 900 mbar to 450 mbar.
T
T_im_Norden11 Jan 2021 21:35I thought the pump was already set to 900?
What were the flow rates at 900?
What were the flow rates at 900?
The system was running continuously at 900 mbar, but it briefly dropped to 200 mbar, at which point I suddenly had a malfunction in the system. Now I have set it to 450 mbar.
At 900 mbar, I get a flow rate of 729 liters per hour (l/h) when the WC and utility hot water circuits are throttled... When all circuits are open, the flow is about 748 l/h at 900 mbar.
Currently, the pump shows a flow of 729 l/h at 450 mbar.
Now here’s the interesting part: when I use the ERR to close the three living room circuits, two kitchen circuits, two hallway circuits, and the utility room including the WC, the total flow drops to 493 l/h, but the flow to the remaining open circuits (bathroom, 2 guest rooms, and 2 bedrooms) increases to about 2 liters per minute (l/min). Without ERR, with all circuits fully open, the flow is only about 1 l/min everywhere (if at all), or just under 1.5 l/min.
This brings me back to my theory with the ERR: the short heating circuits / smaller rooms heat up the fastest, so the actuator closes the valve via ERR. As a result, the next remaining short circuit receives more water, and this continues until all rooms are heated and all actuators / heating circuits are closed. This causes the pressure in the system to rise until eventually the bypass valve opens. This then causes the return temperature to approach the supply temperature, and the system switches off?
I’ll try this tomorrow. Worst case scenario, the system starts cycling.
At 900 mbar, I get a flow rate of 729 liters per hour (l/h) when the WC and utility hot water circuits are throttled... When all circuits are open, the flow is about 748 l/h at 900 mbar.
Currently, the pump shows a flow of 729 l/h at 450 mbar.
Now here’s the interesting part: when I use the ERR to close the three living room circuits, two kitchen circuits, two hallway circuits, and the utility room including the WC, the total flow drops to 493 l/h, but the flow to the remaining open circuits (bathroom, 2 guest rooms, and 2 bedrooms) increases to about 2 liters per minute (l/min). Without ERR, with all circuits fully open, the flow is only about 1 l/min everywhere (if at all), or just under 1.5 l/min.
This brings me back to my theory with the ERR: the short heating circuits / smaller rooms heat up the fastest, so the actuator closes the valve via ERR. As a result, the next remaining short circuit receives more water, and this continues until all rooms are heated and all actuators / heating circuits are closed. This causes the pressure in the system to rise until eventually the bypass valve opens. This then causes the return temperature to approach the supply temperature, and the system switches off?
I’ll try this tomorrow. Worst case scenario, the system starts cycling.