I am currently trying to optimize or fundamentally adjust the hydraulic and thermal balancing of my air-to-water heat pump system, including underfloor heating, but I am running into the following issues:
First, about the house: KfW-55 bungalow with controlled mechanical ventilation
Nearly 105 m2 (1130 ft²) of heated floor area
Air-to-water heat pump with underfloor heating throughout, 10cm (5 inches) pipe spacing, max 30°C (86°F) flow temperature. At -12°C (10°F) outside temperature, the calculated heating load is 3276 watts.
According to the datasheet, the heat pump delivers 3200 watts at -10°C (14°F) outside temperature with flow 35°C (95°F) and return 30°C (86°F).
All rooms are designed for 20°C (68°F), including the bathroom (to avoid an oversized heat pump by the general contractor). Additionally, for the bathroom, an electric radiator is planned to achieve a room temperature of 2°C (4°F) higher than the rest. However, in reality, the toilet, utility room, bedroom, and guest room should only be heated to 18°C (64°F) (it won’t be much lower in a new building). The bathroom is intended to be warmer, at around 21–22°C (70–72°F).
Currently, I have the following questions (though perhaps I am too focused on the self-regulation effect and avoiding actuator valves):
1. Circulation pump: Various guides, manuals, and forum posts recommend setting the circulation pump of the underfloor heating to a constant flow rate.
My conclusion: my circulation pump is a high-efficiency variable-speed pump, so I can set the flow rate on the manifold in L/min (based on the calculations from the general contractor / heating engineer) to whatever I want, but the flow always settles around 600–630 L/h (10–11 L/min). The only significant flow changes I get are when I activate the actuators and room thermostats, which then open or close the valves. The only adjustment parameter on the circulation pump is the minimum flow rate; no other settings are available. But I don’t fully understand how this function works.
2. Operating times of the heat pump / self-regulation: I usually read that the heat pump should run as long as possible, though some sources say short cycling a few times is normal.
My conclusion: if I run the system without actuators and room thermostats, the energy integral control does not work; the system basically runs almost 24/7 at low temperatures, with interruptions only for defrosting. As a result, with a flow temperature of 27°C (81°F), I only get about 19–20°C (66–68°F) room temperature, but I’d prefer around 21–23°C (70–73°F), especially in the bathroom. If I do it the other way, with energy integral control (EIC) and actuators and slightly higher curve so that 30°C (86°F) flow is demanded, the actuators close in the first rooms, which causes the flow to increase to the other rooms because the pump still distributes the volume flow among the remaining open valves. At the same time, the flow temperature rises for rooms where the actuators are still open until the desired temperature is reached and the actuators close. Then the energy integral kicks in and goes negative because actual flow temperature exceeds setpoint flow temperature, until the heat pump shuts off once the energy integral has been reduced.
So right now, I’m struggling with what is better: should the system just run steadily at a flow temperature of 27°C (81°F) (which I might still optimize a bit), with heating only interrupted for defrosting or when the compressor’s hysteresis is exceeded, causing the compressor to be locked out for a certain time? Or should I define time windows during which the system is allowed to operate?
Maybe I could manage this better by refining the balancing, but I guess I’ll have to throttle down so much for the energy integral to work that the flow rate will fall below the minimum required, and the bypass valve will open.
Or should I run the system at 30°C (86°F) flow with room thermostats and actuators, allowing the energy integral control to function properly and reach the desired room temperatures?
Another strange issue is: according to the heating load and underfloor heating calculations, the system requires about 840 L/h (14 L/min) at 4.4 K (7.9°F) delta T in the design case. If I set the flow according to this calculation or slightly lower, the pump only delivers 600–630 L/h (10–11 L/min) at a delta T of about 3–4 K (5.4–7.2°F).
According to the datasheet, the optimal flow rate for the heat pump is 540 L/h (9 L/min) at 5 K (9°F) delta T.
540 L/h * 5 K * 1.163 = 3132 watts
620 L/h * 3.5 K * 1.163 = 2527 watts
840 L/h * 4.4 K * 1.163 = 4287 watts
Calculated heating load at -12°C (10°F) = 3176 watts (and this heating load is probably overestimated since controlled mechanical ventilation was not included in the calculation, and I want only 15–18°C (59–64°F) in four rooms instead of the calculated 20°C (68°F). Also, average outside temperatures for the heat pump in my area are closer to -10°C (14°F) rather than -12°C (10°F), so there is some margin).
Maybe I have now gotten too caught up in theoretical and calculated values and can’t see the forest for the trees?
I would keep the temperature everywhere around 21°C-22°C (70°F-72°F) for now. If the heating curve stays the same, the next step would be to slightly reduce the temperatures in the guest bathroom and utility room.
For the guest bathroom, 18°C (64°F) would be sufficient, and the utility room could go as low as 15°C (59°F). If that works out, then I would adjust the hallway to around 21°C-22°C (70°F-72°F) to bring it closer to 20°C (68°F).
The living room can remain at 21°C-22°C (70°F-72°F) for now.
The guest bedroom and bedrooms are currently around 20.5°C-21°C (69°F-70°F). For those, 18°C (64°F) would also be enough, although I’m still undecided and might keep it at 20°C (68°F) because of the bathroom located between them. I’m considering using an ERR system there, so the guest bedroom and bedrooms would be at least 20°C (68°F) and I could lower the temperature with the ERR if needed. This would be preferable to heating both rooms through the bathroom if I reduce the heating too much. But that is something for the future.
So, this morning it was about -5°C (23°F) outside according to the forecast, and you can notice in some rooms that it feels slightly cooler, for example 20.5°C (69°F) instead of 21.3°C (70°F) or so... However, it’s still not too cold.
I’m going to wait until this evening or tomorrow morning to see how it develops, hoping that the -5°C (23°F) holds or that the outside temperature drops even further.
If everything stays like this, based on the heating curve, it seems to me that I wouldn’t need to reduce the settings much, if at all?
T_im_Norden11 Jan 2021 07:09If it is still too warm in the reference room, you can lower the desired temperature further.
Otherwise, I would adjust the rooms that feel too warm one at a time.
Wait again for some time and make only small adjustments, one room at a time.
I can tell that you already have a good understanding of the heating system and its effects.
Yes, a feeling of how the system works is slowly developing.
Yesterday, my theory about the volume flow regulating pump was almost confirmed.
I started by throttling the guest bathroom and utility room circuits, so that both loops are nearly closed or have minimal flow. This reduced the total system flow rate by about 20 liters per hour (0.09 gallons per minute).
However, what I actually want to achieve is that the liters I throttle somewhere else are redirected to another heating circuit that still has too little flow. A classic example would be the bathroom. Since this is not happening, throttling more doesn’t make sense, because I’m not gaining anything except a further reduction of the total flow rate.
If I keep the heating curve as it is, I only need to throttle a few rooms and the total flow rate is reduced less.
If I increase the heating curve again, I will have to throttle more rooms and more flow, but I don’t gain anything except that the system ends up running at a higher heating curve with less flow.
That’s why I want to run another test with a functioning electronic radiator regulator (ERR) and actuators.
T_im_Norden11 Jan 2021 08:44You can definitely increase the flow rate in your heat pump system if needed; ask the builder or the manufacturer how to adjust it.
I would leave the error as it is because they would only shut off the circuit for you.
Reducing the flow to lower the temperature in the rooms does help since the heat pump has to heat less.
T_im_Norden11 Jan 2021 08:54What is the maximum head height of your pump?