ᐅ Air-to-Water Heat Pump: Current Consumption and Data

Created on: 29 Sep 2020 11:06
B
Bookstar
Hello!
I'll start.
Heated area 200m2 (2,153 sq ft)
KfW 55 standard
Mechanical ventilation with heat recovery
Current outdoor temperature 6°C (43°F)
Heating energy consumption including hot water 35 kWh
Electricity consumption 9 kWh
COP 3.88
H
halmi
21 Jan 2021 14:01
And what flow rate does the efficiency pump show you?

I just looked at about 10 different .dtas files from your heat pump model, and no one really has such a high temperature spread. Your supply temperature is sometimes almost 40°C (104°F)...
Z
Zaba12
21 Jan 2021 14:05
halmi schrieb:

And what flow rate does the efficiency pump show you?

I just looked at about 10 different .dtas from your heat pump model, and nobody really has such a high temperature difference; your supply temperature is sometimes almost 40°C (104°F)...

It can’t display that. Yes, I know, I have noticed that too.
T
T_im_Norden
21 Jan 2021 15:21
How often does it start per day?
If it has been heating continuously for 7 hours, it can’t be that often.
Z
Zaba12
21 Jan 2021 15:35
T_im_Norden schrieb:

How often does it start per day?
If it has been heating continuously for 7 hours, it can’t be that often.

The last heating cycle on the right is "normal"

- no divergence during standby
- the supply and return curves come back together completely after the heating operation ends.

Everything else to the left is unusual and unnecessarily prolongs the heating operation, shortens the intervals between cycles, and makes the operation "expensive."

Basically, the blue and red curves must fully match except during heating operation and hot water production.


Multiple time series graphs with temperature TA and control profiles; arrow marks spike.
D
Daniel-Sp
21 Jan 2021 15:56
Zaba12 schrieb:

The last heating cycle on the right is "normal"

- No spread during standby
- The return and supply curves fully align again from the end of the heating operation.

Everything else to the left is unusual, unnecessarily extending the heating operation, shortening the breaks in between, and making the operation "expensive."

Basically, the blue and red curves must fully match except during heating operation and domestic hot water.

At the marked point, was the heating element active? I can’t clearly tell from the graph.
In the AI/Novelan heat pumps, didn’t you suspect a defective return sensor?
Z
Zaba12
21 Jan 2021 16:17
Daniel-Sp schrieb:

At the marked point, was the heating element active? I can't clearly see it in the graph.
In the AI/Novelan heat pumps, didn't you suspect a faulty return flow sensor?
Yes, in the end the heating element activated there at over 40°C (104°F) supply temperature with a temperature spread of more than 15K.

Yes, it did, but somehow my requests for help there are being ignored.