ᐅ Dimensional Accuracy of Drywall Partitions in Prefabricated Houses

Created on: 22 Feb 2013 13:28
L
luffi1
L
luffi1
22 Feb 2013 13:28
Hello, I have a prefabricated house from a German company, where the interior walls are framed with 10 cm (4 inches) studs and the exterior walls with 16 cm (6.3 inches) studs. The walls are covered with a single layer of drywall on the inside and a double layer with a service cavity on the outside. The drywall panels used are 18 mm (0.7 inches) thick. Some walls show a bulge of about 5 to 10 mm (0.2 to 0.4 inches) on the individual panels when checked horizontally with a spirit level over 62.5 cm (25 inches). What are the usual tolerances for this? Or does it improve once the house has been heated thoroughly?
B
Bibo
17 Mar 2013 13:27
Hello luffi1,

just try searching for DIN 18201 and DIN 18202 regarding dimensional tolerances.
For "finished surfaces of walls and undersides of ceilings," deviations up to 5 mm (0.2 inches) over a measuring length of 1 m (3.3 feet) are allowed. Proper measuring is important, though!
A deviation of 5-10 mm (0.2-0.4 inches) over 62.5 cm (25 inches) would definitely be a visible defect that I would claim.
I would not expect improvement through heating.