Hello dear forum,
We are building a prefabricated house with a ventilation system. Today we had our blower door test, and the result was n50=1.13. The site manager said this is within the standard (max. 1.5). Regarding the conditions:
The building envelope is in place, but the skirt is still missing—that is, the material that is attached to the base slab.
What do you think about this value? As the homeowner, do I have the option to request an improvement in the result?
Thanks and best regards
We are building a prefabricated house with a ventilation system. Today we had our blower door test, and the result was n50=1.13. The site manager said this is within the standard (max. 1.5). Regarding the conditions:
The building envelope is in place, but the skirt is still missing—that is, the material that is attached to the base slab.
What do you think about this value? As the homeowner, do I have the option to request an improvement in the result?
Thanks and best regards
Silent802 schrieb:
Exactly, not good... I need to be able to do something to improve the value, right?! First, I would calculate how much energy is actually being "lost" due to the "leakage." Then, project that amount over the planned service life of the house using realistic heating cost increases. That will give you a total sum you could potentially spend on improvement measures. A rough estimate.
Silent802 schrieb:
I was thinking about hiring an engineer from the city to look for more leaks... Let’s assume a cost-effective building physicist without measuring equipment. They probably won’t charge less than €120 per hour. For my modest energy-saving regulation-compliant home, that equals about three monthly gas installments.
Silent802 schrieb:
Yes, KfW 40 with a ventilation system. Yes, exactly, not good... I should be able to do something to improve the rating, right?!I don’t understand: the noticeable and visible defects are corrected during the blower door test, or at least identified and then fixed afterward.
In our case, for example, the drywall contractor sealed the holes during the process. A roller shutter box was leaking and was fixed later. The missing window sills definitely also boosted the rating somewhat. Nevertheless, an average good value was achieved.
BauBob7 schrieb:
I don’t want to dive into the standards now, but Google tells me that the maximum value would be 1.0 for new buildings with mechanical ventilation systems!?Wasn’t it 1.5? Hm...
As far as I know, it’s only pass or fail. In the latter case, a second blower door test is carried out after locating and fixing the leaks.
Do you already have window sills?
Would there be any other consequences regarding KfW 40 or something for you, or are you just annoyed by it?
Snowy36 schrieb:
this is like passing an exam with a grade of 4.0... As long as the quality criterion is simply pass or fail, it doesn’t really matter in practice whether you passed with a grade of 1.0 or 4.0.
As long as the limit value (1.5 is familiar to me here as well, without wanting to insist on this based on current standards) is met, everything is fine. Unless you have made special agreements beyond that, I see no reason or basis to have your construction supervisor make any corrections that are not defects.
B
boxandroof1 Feb 2019 22:28ypg schrieb:
I don’t understand: the noticeable and visible defects are supposed to be fixed during the blower door testObviously, that didn’t happen, otherwise the value would be different. The blower door test was passed, but the value indicates possible defects.We passed twice because I conducted two tests.
@TE: First, check whether the chimney was sealed.