ᐅ Requirements for Temporary Power Distribution Boxes / Construction Site Power Panels

Created on: 7 Oct 2022 13:05
O
Oberhäslich
O
Oberhäslich
7 Oct 2022 13:05
Unfortunately, I couldn’t find anything suitable in the search…

Since May 2021, there is a new VDE regulation regarding temporary site power distribution boxes. They must be equipped with Type B RCDs and a main switch. The box must also be lockable. Before that, between 2018 and 2021, there was a transitional period. So far, so good.

I’m now looking for a used site power distribution box on eBay Kleinanzeigen. Unfortunately, it seems that all of them still have the older Type A installed. I’d rather not upgrade, as an RCD typically costs between 100-200€ (about $110-$220) depending on the brand, plus installation.

Now I have a good offer through classified ads. According to the seller, the box was connected by an electrician as late as July 2021, i.e., after the transitional period. I looked up the RCDs and both seem to be older models, not Type B. At least the box has a main switch.

The seller said, based on his electrician, that for private building projects it is not relevant whether Type B is installed; this requirement only applies to commercial construction. I’m unfortunately not an expert and feel doubly uncertain. I’d preferably not buy a box that I can’t have connected later. Does anyone have advice? I haven’t engaged an electrician yet.
S
SaniererNRW123
7 Oct 2022 14:07
Oberhäslich schrieb:

The seller said, according to his electrician, that for private construction projects it doesn’t matter whether a Type B RCD is installed; this is only required in commercial construction. Unfortunately, I’m not an expert and feel even more uncertain. I’d rather not buy a panel that I can’t connect properly. Does anyone have advice? I don’t have an electrician lined up yet.

Safety notice: Three-phase sockets (CEE 16A-63A, 400V) require Type B RCDs.

As far as I know, the regulations apply to “construction sites.” There is no distinction between private or commercial work – a developer with multiple houses is also a commercial construction site, right? So it depends on what types of sockets need to be protected (see screenshot).
O
Oberhäslich
7 Oct 2022 14:45
They are the standard 2x 16A and 1x 32A outlets commonly found in a typical distribution board. Therefore, it is not permitted and, in fact, the electrician should not approve it, correct?
S
SaniererNRW123
7 Oct 2022 14:50
Here is the translation:
Oberhäslich schrieb:

These are the usual 2x 16A and 1x 32A circuits, as you would find in a standard distribution board. Therefore, this is not compliant and should actually not be approved by the electrician, correct?
If a device with a frequency converter is connected, then no approval. If not, then it is acceptable. The simple Schuko sockets for the Hilti would be fine in that case.
O
Oberhäslich
7 Oct 2022 14:55
I read somewhere that construction cranes use these types of frequency converters. And since there is one for the bricks/beams, it is likely.
S
SaniererNRW123
7 Oct 2022 15:15
And why not just buy the temporary construction power box, install the RCD, and then sell it again after the construction is done? Honestly, I don’t understand your question. In the end, you’re only losing about 20€ in value. What’s the problem? Just do it and don’t haggle over the last 20€ 😉 It will definitely be cheaper than renting from the electrician.