ᐅ What supply water temperatures are you currently using?

Created on: 24 Oct 2021 10:27
L
lesmue79
Just out of curiosity, to better understand the slope of the heating curve, what flow temperatures do you typically run at 0°C (32°F) outdoor temperature, given a certain indoor temperature and insulation level, when using a combination of underfloor heating and a heat pump?

Background of the question:

My logic tells me that if I want, for example, 22°C (72°F) room temperature, the flow temperature must be at least 22°C (72°F) or higher, since I learned that there needs to be a temperature difference for heat transfer to occur.

So if my heating system turns on at 12°C (54°F) outdoor temperature, my flow temperature should logically start somewhere around 22°C–25°C (72°F–77°F). Accordingly, at only 5°C (41°F) outside, it should be around 27°C (81°F), and at 0°C (32°F) close to 30°C (86°F).

The system design usually takes the location and outdoor temperature down to about –12°C (10°F). If at 0°C (32°F) flow temperature is already 30°C (86°F) according to my logic, then at –12°C (10°F) the flow temperature should be about 40°C (104°F). But most underfloor heating designs for heat pumps are based on a maximum flow temperature of 35°C (95°F).

Of course, the insulation of the house and the indoor temperatures still play a role. Or is the increase in flow temperature actually so gradual that it only rises by about 0.5–1°C (1–2°F) for outdoor temperature drops in 0–5°C (0–9°F) increments?
A
Alessandro
19 Nov 2021 14:43
Malz1902 schrieb:

Quick question: I lowered my heating curve from 0.16 to 0.1. Now the heat pump cycles 15 times in 24 hours at an outdoor temperature averaging 7°C (45°F).
With a heating curve of 0.16 and the same outdoor temperature, it cycled only 3-4 times. Which is better: a lower heating curve with more cycling, or a slightly higher heating curve with less cycling?

15 cycles at 7°C (45°F) outdoor temperature are perfectly fine! There’s no need to worry about that...
D
Daniel-Sp
19 Nov 2021 17:22
Alessandro schrieb:

15 times at 7°C (45°F) indoor temperature are absolutely fine! No need to worry about that...
I see it differently...



More explanation is needed
D
driver55
19 Nov 2021 17:41
The system first needs to be properly adjusted, then you will automatically reach the "correct" number of starts.
Malz1902 schrieb:

I raised the heating curve from 0.2 to 0.24,
Malz1902 schrieb:

Lowered the heating curve again, from 0.16 to 0.1.
🙄
The heating curve alone doesn’t say "squat." You need all relevant parameters.
M
Malz1902
19 Nov 2021 17:51
driver55 schrieb:

The system first needs to be properly adjusted; then you automatically reach the "correct" number of starts.

🙄
The heating curve alone doesn't say anything at all. You need all the relevant parameters.
Which ones do you need or would you like to have?

I think that with a heating curve of 0.16 and only 3 cycles in 24 hours, it’s already well adjusted. Changing from 0.16 to 0.1 only changed the indoor temperature by 0.1 degrees.
OWLer19 Nov 2021 20:47
Malz1902 schrieb:

The change from 0.16 to 0.1 caused the indoor temperature to change by 0.1 degrees

At what outdoor temperature? A change of 0.1 sounds really ambitious. I’m curious to hear your experience during the frost next week!
M
Malz1902
20 Nov 2021 19:20
OWLer schrieb:

At what outside temperature? 0.1 sounds really ambitious. I’m looking forward to your experience report during the frost next week!
At an average temperature over 24 hours currently at 5°C (41°F) and everything is fine, but I’m also curious about subzero temperatures.