ᐅ Ground Source Heat Pump for a 200 m² Single-Family Home with Underfloor Heating, KfW55 Standard – Settings and Optimization
Created on: 4 Nov 2021 20:21
G
grericht
Hello. We moved into our new single-family house in March. I didn’t make any adjustments to the heating system at that time. Now that the temperatures are rising, I’ve started to take a closer look at it.
House details:
Heating system details (descriptions from the invoice):
My previous attempts:
Questions:
Personal preferences:



House details:
- Single-family house with a (heated) basement + 2.5 floors (usable gable roof/also underfloor heating) -> 4 heating circuits
- approximately 200 m² (2150 sq ft) of underfloor heating
- 2 bathrooms WITHOUT additional heating
- kfw55 energy standard
- ventilation system with heat recovery
- Currently 2 rooms in the basement are unoccupied/unutilized + the technical room
- There are also 2 children’s rooms in the attic that are unoccupied/unutilized
Heating system details (descriptions from the invoice):
- High-efficiency brine/water heat pump Dimplex SI 8TU
- High-efficiency brine system SZB 140E for brine/water heat pump with electronically controlled brine circulation pump Yonos Para 25/1-10
- Multifunctional storage tank Geysir MTL-WP650 efficiency class B (150 mm (6 inches) insulation thickness) with connection options for multiple heat generators, with layering plate for large volume flows, capacity 850 liters (225 gallons), domestic hot water preparation using counterflow principle with stainless steel heat exchanger, including differential temperature controller and flow sensor for hot water tapping system
- Hydraulic connection of the heat pump to the multifunctional storage tank with precision steel pipe 28x1.5 mm (1.1x0.06 inch) including insulation, 1 zone charging pump Dimplex UPH 75-25P with shut-off set, switchable between heating and domestic hot water charging
- Integration of the heating system with heating circuit sets Easyflow DN 25 R1" with EPP insulation type 2 including 3-way mixing valve, mixing valve actuator and circulation pump Grundfos UPM3 Auto
- (ERR in 3/4 of the rooms) - currently switched off
- Cooling station Dimplex PKS 14 Econ for passive cooling via geothermal probes, consisting of heat exchanger, brine circulation pump, cooling modules for network operation with heat pump manager and temperature sensor
- Room temperature controller Dimplex Smart RTC, for optimizing weather-compensated control via a reference room
My previous attempts:
- Domestic Hot Water:
- I first focused on the domestic hot water preparation. Initially, it was set to 50°C (122°F) with a 2° hysteresis. For Dimplex, this means that heating started again at 48°C (118°F). This setup was basically fine, but even without any hot water use, heating occurred 2-3 times a day. Since the pump ran only very briefly, the average summer consumption was about 0.7 kWh/day.
- I then experimented with lowering the temperature, setting lockout periods, and increasing the hysteresis. Our "optimal consumption" turned out to be 50°C (122°F) and 7° hysteresis with lockout from 8 pm to 5 pm. This sometimes resulted in the pump not running for an entire day. However, energy use was only reduced to 0.5 kWh/day, meaning hardly any consumption reduction at the cost of noticeable comfort reductions. Currently, I am at 48°C (118°F) and 4° hysteresis with lockout from 10 pm to 5 pm. Since we mostly use hot water in the evening, this works well. For bathing or higher demand, the water is reheated if necessary. I am currently experimenting with 5 or 6 degrees hysteresis, as the heat loss during ongoing heating operation seems lower and we might be able to skip a day sometimes. We’ll see...
- Now, regarding the heating, my attempts:
- All ERRs switched off, heating circuits opened roughly by feel, and tried to adjust by regulation. Control was via fixed return flow temperature, which I tested between 23 and 26°C (73°F and 79°F). The consumption and COP results were very satisfactory. Unfortunately, I couldn’t get the bathroom above 22°C (72°F) without other rooms becoming too warm (rooms quickly reached 22°C, which I find too high).
- Turned the ERR back on in the children’s rooms.
- After a one-week vacation during which I completely switched off the heating, I started over. I tried the recommended approach of fully opening the warmest room (bathroom) to about 2.2 liters/min (0.58 gallons/min) and then increasing the temperature until satisfied. But this meant the heating was massively oversized?! The heat pump came on about 20 times for 10-15 minutes each, the supply temperature was nicely between 30 and 33°C (86°F and 91°F) but the temperature felt like it never really got away from the heat pump’s threshold. I am attaching a picture of the behavior.
- Suspecting insufficient flow and hesitant to adjust the heating pump, I slowly opened other rooms slightly.
- I also tried increasing the fixed temperature to 27 or 28°C (81°F or 82°F) and used hysteresis to make the pump run less often but longer. I am now quite satisfied with the temperatures in the house. However, the numbers still look a bit odd to me. I believe there are now many rooms/areas/storage volumes with such low flow that “cooled down” mass just circulates in the loop and eventually reaches the return line repeatedly. I don’t mind that but I also do not want to risk any damage. I will attach another picture.
- Lastly, I reduced the temperature at night and in the morning so the heating starts at favorable times. Currently, two starts of about 2-3 hours each are sufficient.
Questions:
- Am I completely off track here or are these approaches generally valid? Unfortunately, I can’t really rely on the heating engineer. He is surely competent but firstly hardly reachable and secondly probably overwhelmed by such optimization considerations.
- What about rooms that are unused? Should I use the screed as a buffer and keep them slightly heated (<0.5 liters/min (0.13 gallons/min)) anyway?
- I increasingly believe that managing the large temperature difference between the bathroom at 23°C (73°F) and the rooms at 20.5°C (69°F) is not well controlled – is there really no alternative to an additional heat source? We only use the bathroom for about 2 hours and in the evening for 4 hours at 23°C (73°F). Otherwise, 21-22°C (70-72°F) would definitely be sufficient there.
- Any tips on settings?
Personal preferences:
- The underfloor heating is off in the bedroom – yet it quickly reaches 19-20°C (66-68°F), which is almost too warm.
- In the 3 children’s rooms, the ERR closes from 5 pm to 3 am (for sleeping – with time delay)
- Other rooms 20-21°C (68-70°F)
- Open-plan kitchen/living room 21-22°C (70-72°F)
- Bathrooms 23°C (73°F)
B
Benutzer2009 Nov 2021 11:23halmi schrieb:
Just two adults lying in bed produce about 400 watts,Maybe for 25 minutes 😎, but otherwise the average person is around 120 watts (awake/during the day). In a resting state it’s about 80 watts. Under the blanket at night it’s the same, but thanks to ceiling insulation, even less heat actually reaches the room.halmi schrieb:
I can’t quite understand how those temperature values are reached inside the house. Yesterday, both floor-to-ceiling windows in the bedroom were left tilted open by mistake, and we still had "only" 19°C (66°F) in the bedroom. Just two adults lying in bed produce around 400 watts, which should noticeably raise the temperature in any new build after 6-8 hours.
The ventilation system alone already stabilizes the temperature relatively well inside the house, or don’t you have one?Which values are you referring to? For me, before airing it’s around 20°C (68°F) and after airing between 18.5°C and 19.5°C (65°F and 67°F), depending on the duration and outside temperature. I also don’t quite get how you can end up with 16°C (61°F) during airing. At near zero degrees outside, I would probably have to leave it open for half a day.By the way, I’m also calming down a bit right now. I recalculated more precisely and now come to almost 5 as the COP for all heating consumers including distribution in the house. And we probably still haven’t reached average winter temperatures yet. The compressor now consumes about 10 kWh/day, but then the other consumers weigh less. However, it could well be that after the winter I end up somewhere around 4.5.
grericht schrieb:
Including electricity for the heating pump and the heat pump control? Your numbers are similar to mine. But I just read that the distribution through the heating system also needs to be considered. For me, that's about an additional 35W for the heating pump (which runs during subzero temperatures), 25W standby for the heat pump, ERR+-valves, and the other pumps + heating pump running while heating draw even 255W. This means I have at least 25W running continuously, the heating pump at 35W runs about 15% of the time at ambient temperatures above 5°C (41°F) and 100% below 5°C (41°F), and about 6 hours per day the 255W load is added. Roughly, this amounts to around 2kWh on heating days (probably more), 0.7kWh on summer days, and about 1–1.5kWh in passive cooling mode. This naturally lowers the COP significantly, especially for hot water. We have a Viessmann compact unit. It includes hot water and all kinds of pumps inside. Around it, we have nothing—no buffer tank, no additional pump, no circulation, nothing. ERR valves are normally open without power, so they also don't consume electricity. Since we don’t have a separate heat pump meter, our COP values come from the Viessmann heat pump itself. Because everything is integrated there, I sincerely hope that pump electricity and similar loads are included. Of course, I cannot say exactly how accurate these figures are.
Based on the total consumption (which I get from the photovoltaic portal), I estimate a base load of about 150kWh per month, plus around 25kWh each for hot water and ventilation. When the heating is on, monthly consumption increases by about 100kWh during transitional seasons—and naturally more during harsh subzero temperatures. Overall, this year we expect about 1,800–2,000kWh of heating electricity for 170m² (about 1,830ft²) and two people, plus 300kWh for hot water (including all pumps)... No idea if that’s a lot.
Hangman schrieb:
We have a Viessmann compact unit. It includes domestic hot water and various pumps all integrated. Outside of that, we have nothing else—no buffer tank, no additional pump, no circulation, nothing. The ERR valves are electrically open without power, so they don't consume electricity. Since we don’t have a separate heat pump meter, our COP values come directly from the Viessmann heat pump itself. And because everything is integrated there, I hope the pump electricity consumption and so on are included. I don’t know exactly how accurate these values are.
Based on the total consumption (which I get from the photovoltaic portal), I assume we have about 150 kWh base load per month plus about 25 kWh each for hot water and ventilation. Once the heating is on, the monthly consumption increases by around 100 kWh during the transition periods—of course, more during severe subzero temperatures. In total, this year we expect about 1,800–2,000 kWh heating electricity plus 300 kWh for hot water (including all pumps) for 170 sqm (about 1,830 sq ft) and two people... no idea if that’s much. My heat pump "measures" not only the heating and hot water heat output but also the “environmental energy.” I assume this is an estimate based on the device having a certain COP, and it then calculates the environmental energy “extracted” from the produced heat amount. I believe these are purely estimated values, and I think your system is similar. I wouldn’t expect your unit to have an electricity consumption meter. Although, for you, it would be quite easy to add a consumption meter and then determine the actual seasonal performance factor (SPF).
For comparison, I hope and think that for 5 people in 200 sqm (about 2,150 sq ft) with 2 bathrooms, we will use around 2,000 kWh over a year including ventilation. It will be interesting to see.
Two questions remain unanswered, and I would be very grateful if someone could address them:
- Do you know or can you guess how the heat pump determines the heat produced? Are these estimates or measurements? If measurements, are they calibrated and reliable or just approximate as a reference? If not calibrated and reliable: how is the seasonal performance factor calculated then, since the produced heat amount is essential for that?!
- Does it make sense to not heat completely unused rooms? This concerns individual unused rooms in the basement—not leaving the entire basement cold—and also the bedroom, which ideally should stay as cool as possible.