ᐅ Ground Source Heat Pump for a 200 m² Single-Family Home with Underfloor Heating, KfW55 Standard – Settings and Optimization
Created on: 4 Nov 2021 20:21
G
grericht
Hello. We moved into our new single-family house in March. I didn’t make any adjustments to the heating system at that time. Now that the temperatures are rising, I’ve started to take a closer look at it.
House details:
Heating system details (descriptions from the invoice):
My previous attempts:
Questions:
Personal preferences:



House details:
- Single-family house with a (heated) basement + 2.5 floors (usable gable roof/also underfloor heating) -> 4 heating circuits
- approximately 200 m² (2150 sq ft) of underfloor heating
- 2 bathrooms WITHOUT additional heating
- kfw55 energy standard
- ventilation system with heat recovery
- Currently 2 rooms in the basement are unoccupied/unutilized + the technical room
- There are also 2 children’s rooms in the attic that are unoccupied/unutilized
Heating system details (descriptions from the invoice):
- High-efficiency brine/water heat pump Dimplex SI 8TU
- High-efficiency brine system SZB 140E for brine/water heat pump with electronically controlled brine circulation pump Yonos Para 25/1-10
- Multifunctional storage tank Geysir MTL-WP650 efficiency class B (150 mm (6 inches) insulation thickness) with connection options for multiple heat generators, with layering plate for large volume flows, capacity 850 liters (225 gallons), domestic hot water preparation using counterflow principle with stainless steel heat exchanger, including differential temperature controller and flow sensor for hot water tapping system
- Hydraulic connection of the heat pump to the multifunctional storage tank with precision steel pipe 28x1.5 mm (1.1x0.06 inch) including insulation, 1 zone charging pump Dimplex UPH 75-25P with shut-off set, switchable between heating and domestic hot water charging
- Integration of the heating system with heating circuit sets Easyflow DN 25 R1" with EPP insulation type 2 including 3-way mixing valve, mixing valve actuator and circulation pump Grundfos UPM3 Auto
- (ERR in 3/4 of the rooms) - currently switched off
- Cooling station Dimplex PKS 14 Econ for passive cooling via geothermal probes, consisting of heat exchanger, brine circulation pump, cooling modules for network operation with heat pump manager and temperature sensor
- Room temperature controller Dimplex Smart RTC, for optimizing weather-compensated control via a reference room
My previous attempts:
- Domestic Hot Water:
- I first focused on the domestic hot water preparation. Initially, it was set to 50°C (122°F) with a 2° hysteresis. For Dimplex, this means that heating started again at 48°C (118°F). This setup was basically fine, but even without any hot water use, heating occurred 2-3 times a day. Since the pump ran only very briefly, the average summer consumption was about 0.7 kWh/day.
- I then experimented with lowering the temperature, setting lockout periods, and increasing the hysteresis. Our "optimal consumption" turned out to be 50°C (122°F) and 7° hysteresis with lockout from 8 pm to 5 pm. This sometimes resulted in the pump not running for an entire day. However, energy use was only reduced to 0.5 kWh/day, meaning hardly any consumption reduction at the cost of noticeable comfort reductions. Currently, I am at 48°C (118°F) and 4° hysteresis with lockout from 10 pm to 5 pm. Since we mostly use hot water in the evening, this works well. For bathing or higher demand, the water is reheated if necessary. I am currently experimenting with 5 or 6 degrees hysteresis, as the heat loss during ongoing heating operation seems lower and we might be able to skip a day sometimes. We’ll see...
- Now, regarding the heating, my attempts:
- All ERRs switched off, heating circuits opened roughly by feel, and tried to adjust by regulation. Control was via fixed return flow temperature, which I tested between 23 and 26°C (73°F and 79°F). The consumption and COP results were very satisfactory. Unfortunately, I couldn’t get the bathroom above 22°C (72°F) without other rooms becoming too warm (rooms quickly reached 22°C, which I find too high).
- Turned the ERR back on in the children’s rooms.
- After a one-week vacation during which I completely switched off the heating, I started over. I tried the recommended approach of fully opening the warmest room (bathroom) to about 2.2 liters/min (0.58 gallons/min) and then increasing the temperature until satisfied. But this meant the heating was massively oversized?! The heat pump came on about 20 times for 10-15 minutes each, the supply temperature was nicely between 30 and 33°C (86°F and 91°F) but the temperature felt like it never really got away from the heat pump’s threshold. I am attaching a picture of the behavior.
- Suspecting insufficient flow and hesitant to adjust the heating pump, I slowly opened other rooms slightly.
- I also tried increasing the fixed temperature to 27 or 28°C (81°F or 82°F) and used hysteresis to make the pump run less often but longer. I am now quite satisfied with the temperatures in the house. However, the numbers still look a bit odd to me. I believe there are now many rooms/areas/storage volumes with such low flow that “cooled down” mass just circulates in the loop and eventually reaches the return line repeatedly. I don’t mind that but I also do not want to risk any damage. I will attach another picture.
- Lastly, I reduced the temperature at night and in the morning so the heating starts at favorable times. Currently, two starts of about 2-3 hours each are sufficient.
Questions:
- Am I completely off track here or are these approaches generally valid? Unfortunately, I can’t really rely on the heating engineer. He is surely competent but firstly hardly reachable and secondly probably overwhelmed by such optimization considerations.
- What about rooms that are unused? Should I use the screed as a buffer and keep them slightly heated (<0.5 liters/min (0.13 gallons/min)) anyway?
- I increasingly believe that managing the large temperature difference between the bathroom at 23°C (73°F) and the rooms at 20.5°C (69°F) is not well controlled – is there really no alternative to an additional heat source? We only use the bathroom for about 2 hours and in the evening for 4 hours at 23°C (73°F). Otherwise, 21-22°C (70-72°F) would definitely be sufficient there.
- Any tips on settings?
Personal preferences:
- The underfloor heating is off in the bedroom – yet it quickly reaches 19-20°C (66-68°F), which is almost too warm.
- In the 3 children’s rooms, the ERR closes from 5 pm to 3 am (for sleeping – with time delay)
- Other rooms 20-21°C (68-70°F)
- Open-plan kitchen/living room 21-22°C (70-72°F)
- Bathrooms 23°C (73°F)
P
Pumpernickel130 Dec 2021 14:23Hello, I’m not sure if this is the right thread for this, but I’ll give it a try anyway.
We are building a single-family house with a ground source heat pump and underfloor heating, and we plan to install a photovoltaic system in the next few years. Now the question arises whether a second electricity meter is necessary. Having a separate meter for the heat pump tariff would make sense. However, our electrician said that if the photovoltaic system is installed, there will only be one electricity meter. We would need to calculate whether a second meter makes sense or not.
I’m totally confused here. How did you handle this? Second electricity meter yes or no, and why? Thanks in advance.
We are building a single-family house with a ground source heat pump and underfloor heating, and we plan to install a photovoltaic system in the next few years. Now the question arises whether a second electricity meter is necessary. Having a separate meter for the heat pump tariff would make sense. However, our electrician said that if the photovoltaic system is installed, there will only be one electricity meter. We would need to calculate whether a second meter makes sense or not.
I’m totally confused here. How did you handle this? Second electricity meter yes or no, and why? Thanks in advance.
R
RotorMotor30 Dec 2021 14:40@Pumpernickel1 doesn’t quite fit here. We only have one meter for everything.
Whether a second meter is worthwhile for you depends on your consumption and the rates offered in your area.
Just do the calculations.
Whether a second meter is worthwhile for you depends on your consumption and the rates offered in your area.
Just do the calculations.
B
Benutzer20030 Dec 2021 14:40Pumpernickel1 schrieb:
We are building a single-family home with a geothermal heat pump and underfloor heating and are planning to install a photovoltaic system in the next few years. Now the question arises whether a second electricity meter is necessary. It would definitely make sense for the heat pump tariff. However, our electrician said that if the photovoltaic system is installed, there will only be one electricity meter. We would need to calculate whether a second electricity meter makes sense or not.
I’m completely lost here. How did you solve it? Second electricity meter yes or no, and why? Thanks in advance. Please use the search function. There are many threads on this topic.
Pumpernickel1 schrieb:
Hello, I’m not sure if this is the right thread, but I’ll give it a try anyway.
We are building a single-family house with a ground source heat pump and underfloor heating, and we plan to install a photovoltaic system in the next few years. Now the question is whether a second electricity meter is necessary. It would make sense for the heat pump tariff. However, our electrician said that when the photovoltaic system is installed, there will only be one electricity meter. You would have to calculate whether a second meter makes sense or not.
I’m completely lost here. How have you solved this? Second meter yes or no, and why? Thanks in advance. So, we have 2 meters and 2 tariffs. We don’t have photovoltaics yet, and I decided to just test it first. I didn’t know beforehand how much heating energy we would use.
As expected, it’s quite close whether it’s worth it—and that’s even without photovoltaics.
With photovoltaics, I would strongly advise against it because that inevitably reduces self-consumption, which is the “most valuable self-generated electricity.” At least, I don’t know of any way to use the same photovoltaic system on two separate electricity circuits for self-consumption. You would have to decide which circuit you want to use the generated electricity for. You can connect it to the heat pump consumption (which doesn’t make much sense because the photovoltaic system generates a lot in summer, but the heat pump needs a lot in winter) or to the household electricity (which means that in summer and possibly even winter, your household electricity would be fully covered by photovoltaics, but the heat pump would run 100% on the heat pump electricity tariff). For me, that risk is too high since you would lose some nice winter sunshine hours that could also support the heat pump’s self-consumption. But that also depends on the type of photovoltaic system you have. If it only generates power from spring to autumn, you could run the heat pump separately. We have a roof angled at 50° facing south, so I expect some output even in winter.
As a last option, you could split your photovoltaic system: use one inverter for the heat pump’s self-consumption part and another for household electricity. I have no idea if there are options to split that more flexibly (for example, almost all photovoltaics go to the heat pump in winter, and in summer about 20% to the heat pump, the rest to household electricity). But the energy supplier must agree to install 2 bidirectional meters. I think they generally reject this (at least for the heat pump electricity tariff, they probably don’t allow it).
And as I said, even for us, the second meter is probably hardly worthwhile (I can say for sure in about 5 months). The (low) basic fees for the second meter almost negate the cheaper kWh rate anyway. But that also depends on how much heating output you generate annually and with what seasonal performance factor. Also consider that the heat pump’s efficiency and comfort decrease because it occasionally hits the utility lockout. So I think from July 1st, we will only have one meter and will calmly approach the photovoltaics topic then.
Here is an update on my heating system:
I have tried different things. I have basically turned off the room thermostats and control valves. I am still working with the thermal balancing method. I called the office that carried out the heating load calculation retroactively for us. So either they did something unusual, or I have often heard it differently before: the heating load of the rooms is the calculation of how much heating energy goes into each room. But when they then calculated the hydraulic balancing, they did not calculate how much heating energy actually comes into the rooms at a certain flow. They only calculated how much flow is needed in each circuit so that a similar heating energy can be supplied to each room at the same time.
Practically:
The heating load in the basement is much lower because only about 15°C (59°F) is required there. But even there, based on pipe spacing and pipe length, they calculated that heating load X can be delivered at time Y, just like in the bathroom and other rooms. This means that hydraulic balancing would only result in the basement being off much more often than the bathroom. But that does me zero good if I don’t have electronic radiator thermostats (ERTs). Therefore, I prefer simpler thermal balancing and am fairly satisfied with it. In the open-plan area, due to the kitchen, many people, and sunlight, there are quite some temperature differences. I am considering activating the ERT there and closing the control valve at a certain temperature.
Question:
Currently, I have control valves that are closed without power (normally closed). That would make no sense here. Do I simply know whether I can replace them with ones that are normally open without power? Are there any recommendations for valves that consume low power? I have 2W devices installed, but I heard there are also ones with 1W? Five circuits/valves are connected to that room.
Regarding consumption: the Coefficient of Performance (COP) has dropped slightly to about 4.75. The annual performance factor has been at 4.35 since May, and I hope to achieve at least 4.4, possibly even 4.5, by the end of the year. The source inlet temperature is now below 5°C (41°F). Let’s see where this goes.
Question:
I only have a temperature difference of about 3°C (5.4°F) from the heat source inlet to outlet. I read that it can actually be 7°C (12.6°F). I have already reduced the pump to level 2 out of 3. That didn’t improve much. At level 1, it seems it no longer has enough power to pump. I then immediately set it back to level 2 because the inlet temperature dropped rapidly and I was afraid it might freeze.
Is this normal?
I have tried different things. I have basically turned off the room thermostats and control valves. I am still working with the thermal balancing method. I called the office that carried out the heating load calculation retroactively for us. So either they did something unusual, or I have often heard it differently before: the heating load of the rooms is the calculation of how much heating energy goes into each room. But when they then calculated the hydraulic balancing, they did not calculate how much heating energy actually comes into the rooms at a certain flow. They only calculated how much flow is needed in each circuit so that a similar heating energy can be supplied to each room at the same time.
Practically:
The heating load in the basement is much lower because only about 15°C (59°F) is required there. But even there, based on pipe spacing and pipe length, they calculated that heating load X can be delivered at time Y, just like in the bathroom and other rooms. This means that hydraulic balancing would only result in the basement being off much more often than the bathroom. But that does me zero good if I don’t have electronic radiator thermostats (ERTs). Therefore, I prefer simpler thermal balancing and am fairly satisfied with it. In the open-plan area, due to the kitchen, many people, and sunlight, there are quite some temperature differences. I am considering activating the ERT there and closing the control valve at a certain temperature.
Question:
Currently, I have control valves that are closed without power (normally closed). That would make no sense here. Do I simply know whether I can replace them with ones that are normally open without power? Are there any recommendations for valves that consume low power? I have 2W devices installed, but I heard there are also ones with 1W? Five circuits/valves are connected to that room.
Regarding consumption: the Coefficient of Performance (COP) has dropped slightly to about 4.75. The annual performance factor has been at 4.35 since May, and I hope to achieve at least 4.4, possibly even 4.5, by the end of the year. The source inlet temperature is now below 5°C (41°F). Let’s see where this goes.
Question:
I only have a temperature difference of about 3°C (5.4°F) from the heat source inlet to outlet. I read that it can actually be 7°C (12.6°F). I have already reduced the pump to level 2 out of 3. That didn’t improve much. At level 1, it seems it no longer has enough power to pump. I then immediately set it back to level 2 because the inlet temperature dropped rapidly and I was afraid it might freeze.
Is this normal?