Hello dear forum,

I have the following problem in my new build.
My temperature sensor is turned all the way down.
However, I can’t tolerate the temperature in the living/dining room.
It is 25 degrees Celsius (77°F) here. How can that be?
I have already lowered the desired temperature setting on my boiler, but it doesn’t help.

I have one heating circuit for the kitchen, one for the dining room, and two for the living room. All open to one room. Is it correct or possible that all heating circuits are controlled by a single temperature sensor, or did they forget to install some?

Thank you very much!
K
kkk272729
27 Feb 2018 10:27
Mycraft schrieb:

that is already covered by the AT regulation.

The AT specifies a possible heat demand, which does not necessarily reflect the actual heat demand, since it is based solely on the outside temperature and does not take other factors into account, such as solar radiation or wind.
K
Knallkörper
27 Feb 2018 10:33
The return temperature can certainly be included as an additional parameter in the control system. However, this only applies if the flow rate is simultaneously measured or remains constant.
M
Malz1902
27 Feb 2018 20:00
What flow rate is recommended for 5 heating circuits? For the living room / dining room / kitchen, is it better to have a high flow rate, around 3 liters (0.8 gallons), or just 1 liter (0.26 gallons)?
K
Knallkörper
27 Feb 2018 20:47
You will need to experiment with this. Rooms with higher heat demand and/or less heating surface should receive maximum flow. These are almost always the bathrooms. You adjust the supply temperature so that the desired temperature is easily reached there (the room thermostat turns off). For the other rooms, reduce the flow gradually until the desired room temperature is no longer achieved, then increase the flow slightly again. This process takes time because the system is very slow to respond, and you should wait at least 24 hours after each adjustment.

For some users, the heat demand on the upper floor is reportedly still higher than on the ground floor, so the flow rate on the ground floor is the lowest.

In the bathrooms, I have 4 liters per minute (l/min), and in all other rooms about 1 liter per minute (l/min).

The documentation from your heating installer should also include the designed flow rates. This can at least serve as a reference point.
M
Malz1902
27 Feb 2018 21:02
Thank you very much for the detailed response.
I have now set the flow rate in the living room / dining area / kitchen to 1 liter per minute (l/min). The room thermostat (RT) is set to level 4. In the bathrooms on the ground floor and upper floor, I have set the flow to maximum. At 3 l/min in both rooms, the RT is set to 6, which means fully on.
N
Nordlys
27 Feb 2018 21:08
Small update after 24 hours of fiddling with the flow control valve.
The apartment is still warm. Showering with 50°C (122°F) instead of 60°C (140°F) hot water works well too. Maybe the risk of Legionella is a bit overestimated? Or what temperature do you set your hot water to?