Hello everyone!
We recently bought a house and now have the following issue:
The heating system is a Eurocontrol KM. In the basement, I have underfloor heating, and on the ground floor, radiators. The radiators work perfectly fine. However, the mixing valve for the underfloor heating does not receive a signal from the heating system to open. If I open the mixing valve manually, the heating system immediately sends a signal to close it.
During the relay test, the mixing valve opens and closes as expected.
The outdoor sensor shows accurate values (currently 4°C (39°F)).
The flow temperature sensor also shows correct values (currently 18°C (64°F)).
For testing, I set the heating curve very high. At 0°C (32°F) outside, the flow temperature should be set to 80°C (176°F).
The heating is set to continuous operation.
When I turn the dial and increase the temperature setpoint from 22°C (72°F) to 24°C (75°F), the mixing valve opens briefly, then closes again. The same happens when I set it to 26°C (79°F). This also occurs in manual mode...
Since I have a heat exchanger, I have a mixing valve (Brötje SQA 31.1) and two circulating pumps (Grundfos Alpha 2 and Brötje CP43). There is no maximum thermostat.
Thanks for your help!
We recently bought a house and now have the following issue:
The heating system is a Eurocontrol KM. In the basement, I have underfloor heating, and on the ground floor, radiators. The radiators work perfectly fine. However, the mixing valve for the underfloor heating does not receive a signal from the heating system to open. If I open the mixing valve manually, the heating system immediately sends a signal to close it.
During the relay test, the mixing valve opens and closes as expected.
The outdoor sensor shows accurate values (currently 4°C (39°F)).
The flow temperature sensor also shows correct values (currently 18°C (64°F)).
For testing, I set the heating curve very high. At 0°C (32°F) outside, the flow temperature should be set to 80°C (176°F).
The heating is set to continuous operation.
When I turn the dial and increase the temperature setpoint from 22°C (72°F) to 24°C (75°F), the mixing valve opens briefly, then closes again. The same happens when I set it to 26°C (79°F). This also occurs in manual mode...
Since I have a heat exchanger, I have a mixing valve (Brötje SQA 31.1) and two circulating pumps (Grundfos Alpha 2 and Brötje CP43). There is no maximum thermostat.
Thanks for your help!