ᐅ Wrong Heating System Installed — Issues and Consequences?
Created on: 29 Feb 2020 17:08
O
opalau
I need your advice: We contractually agreed with our main contractor that the Wolf gas-solar unit CSZ-2-14/300R would be installed in our house. This week, I accidentally discovered that instead, the next larger model, the CSZ-2-20/300R, has been installed. (The house is not finished yet; handover is expected in March.)
As the model names suggest, these units have maximum outputs of 14 kW and 20 kW, respectively. If I understand our energy saving certificate correctly, our house (energy saving regulations, 225 m² (2420 ft²)) has an annual heat demand of 14,987 kWh (11,681 kWh space heating, 3,306 kWh domestic hot water). Lacking technical expertise, I found during some initial research that I can estimate the heating load by dividing annual heating hours (about 2,100 h?) into this. Using this rough calculation, I arrive at a heating load of around 7.1 kW. Is this correct so far, and am I right to assume that this means the 20 kW version is significantly oversized?
Another problem is that the lower modulation limit of the larger boiler is much higher: 4.4 kW compared to 2.1 kW. I’m concerned that especially during transitional seasons, the boiler will cycle more frequently, leading to faster wear and less efficiency overall.
I haven’t been able to speak directly with the installer yet. The construction manager of the main contractor relayed the installer’s explanation that the unit was “sized larger due to the building size.”
I will discuss this with our independent construction expert next week.
So here are my questions:
Is my assumption correct that the 20 kW version is completely oversized?
Is my assumption correct that the higher lower modulation limit is a disadvantage for us?
How would you approach this situation? How serious do you see the issue, and what options do I have?
Thanks for your help
wrobel1 Mar 2020 18:52
Hello
Such a system is not only responsible for heating.
It may therefore be necessary to use the 20 kW version for domestic hot water preparation.
During the construction phase, the bathroom fittings might have been upgraded with a larger bathtub, a rain shower, or an additional bathroom.
Olli
hegi___
1 Mar 2020 18:55
Approximately 0.2 kW of heating power is calculated per person...
So for the remaining 13 kW, you can then produce domestic hot water for 65 people.
guckuck2
1 Mar 2020 18:59
With 20 kW, the system heats water like an electric tankless water heater...
wrobel1 Mar 2020 19:13
Hello
I have learned that the hot water system should be sized according to the demand of the fixtures.
Olli
wrobel1 Mar 2020 19:24
hegi___ schrieb:
You can estimate about 0.2 kW heating capacity per person...
So for the remaining 13 kW, you can produce hot water for 65 people.
Well, if it’s that simple,
then the system would be perfect for the changing rooms of our football club.
Olli
hegi___
1 Mar 2020 19:53
Rule of thumb: 1 kW heats 1000 liters of water by 1 Kelvin in one hour.
22 people x 45 liters (at 38°C (100°F)) = 1000 liters
With a cold water temperature of 8°C (46°F), this results in a delta T of 30 K
13 kW produces 13 K per hour
The storage tank will be charged within 2.3 hours.
So it could work.
It doesn’t matter if the boiler is heated to 55°C (131°F) and thus less hot water is used.