CheckieChan4 Dec 2013 22:11C
CheckieChan4 Dec 2013 23:15How does such a large difference come about?
The spans are almost the same. You should note that the table according to the Eurocode distinguishes between permanent and imposed loads. If you have a permanent load of 0.5 kN/m² and an imposed load of 2 kN/m², the span from the other table with a load of q = 2.5 kN/m² is almost identical.
F
friedrich276 Dec 2013 18:18no, example
Table 1 walkable floor slabs:
- permanent load (screed) 1.5 kN
- live load in category A 2.0 kN
combined total 3.5 kN
maximum span for 12 cm (5 inches) slab
3.8 meters (12.5 feet)
Table 2 3.5 kN
maximum span for 12 cm (5 inches) slab
4.9 meters (16 feet)
In the first table, which is the normal case for you, a distinction is made between static and dynamic loads, self-weight is included, and especially the vibration check is considered.
The second table only addresses deflection, and I’m not sure whether self-weight is included there.
A slab like that may support the load and possibly meet deflection requirements, but if the glasses in the cupboard rattle, that is not very pleasant.
Conclusion: for you as a home builder, only Table 1 is relevant.
By the way, greetings to Allrounder in MOL if you read this. Just can’t resist when something like this comes up.
Table 1 walkable floor slabs:
- permanent load (screed) 1.5 kN
- live load in category A 2.0 kN
combined total 3.5 kN
maximum span for 12 cm (5 inches) slab
3.8 meters (12.5 feet)
Table 2 3.5 kN
maximum span for 12 cm (5 inches) slab
4.9 meters (16 feet)
In the first table, which is the normal case for you, a distinction is made between static and dynamic loads, self-weight is included, and especially the vibration check is considered.
The second table only addresses deflection, and I’m not sure whether self-weight is included there.
A slab like that may support the load and possibly meet deflection requirements, but if the glasses in the cupboard rattle, that is not very pleasant.
Conclusion: for you as a home builder, only Table 1 is relevant.
By the way, greetings to Allrounder in MOL if you read this. Just can’t resist when something like this comes up.
F
friedrich277 Dec 2013 06:43Addition: I am referring here to an apartment ceiling; it is somewhat different with a roof ceiling, as vibration is not relevant there.
What do you see as the purpose of this type of solid wood ceiling?
Best regards
What do you see as the purpose of this type of solid wood ceiling?
Best regards