ᐅ Is a connected load of 14.5 kW sufficient for the house?

Created on: 23 Jun 2020 11:36
T
Tolentino
Dear forum members,

According to the scope of work from my construction supervisor, the connection capacity for the house will be 14.5 kW.
Is that sufficient for a modern single-family home with 5 people?
I understand that most appliances are not necessarily running at the same time, but if I imagine that in winter many devices might be used simultaneously, and then a 2 kW hairdryer is added, the limit could be reached.
What would actually happen in that case?
Is it possible to upgrade the connection capacity, or are there restrictions imposed by the utility company?
How does a photovoltaic system affect this? Can it increase the maximum peak power demand of a house, or is it useless if the electrical installation itself is not designed for higher loads?

Thank you and best regards

Tolentino
G
gmt94
23 Jun 2020 13:17
That will most likely be the SLS in the electrical panel. It comes in different sizes.

The utility usually protects the main service connection with a 63A fuse or breaker. That equals 400V * 63A * square root of 2, which is about 35kW.

Then comes the SLS in the electrical panel, which, as mentioned, is available in different sizes. Most likely, a 25A one will be installed for you, which corresponds to 14kW.

I just checked ours. We have a 35A one, which corresponds to about 20kW.

What happens if you exceed the 14kW is simple: the contactor in the SLS will trip.

You should try to talk to the grid operator to see if you can get a higher rating.
L
Lumpi_LE
23 Jun 2020 13:23
We also have an 11 kW induction cooktop, heat pump, clothes dryer... I think 12 kW was once considered the absolute maximum, but that really requires everything to be used at the same time.
Tolentino23 Jun 2020 13:28
I also think we are talking about rare situations here. You would basically have to be wearing full winter gear and have the cooktop on booster mode, the oven set to 250°C (480°F) with the grill on top and bottom, the hot water tank emptied, and both showers running. Then add the microwave and vacuum cleaner. If the hairdryer (sorry, hot air hair dryer) is also on… you could probably reach around 15 kW.

But I would prefer to have a bit more margin...

And the "larger" SLS fuse is sufficient then? There’s no need to install a "thicker" main supply cable to the house?
G
gmt94
23 Jun 2020 13:32
Warning: dangerous half-knowledge.

I seem to remember that at the time, the network operator's conditions specified a maximum of 100kW. Anything above that would have cost more.

The cable brought into your house is already quite thick.

And GU has no influence at all on the network operator’s connection. That is an issue between the network operator and you.
Tolentino23 Jun 2020 13:35
So I think 100 kW would be more than enough for me.
Actually, even the previously mentioned 35 kW should be sufficient. I just feel uneasy if it would already be critical at 14.5 kW...
G
gmt94
23 Jun 2020 13:38
So I took two pictures.

The "cable thickness" comes from the utility company.


Close-up of a distribution box with brown L cables and green-yellow grounding behind plexiglass


And it goes to the fuse box.

Transparent plastic housing with orange tubing and visible electronic components.


So there is still some room for capacity.

The problem is you never know what will come next, especially regarding electric mobility.