ᐅ What is the maximum screed thickness for underfloor heating?

Created on: 12 Feb 2020 14:46
T
Tx-25
Hello. We are about to install a floating screed for the underfloor heating. The base slab is very uneven, with the level varying between 17.5cm (7 inches) and 19.8cm (7.8 inches). Therefore, the insulation and screed layers need to be planned accordingly. So, I can’t build the height of the construction higher than 17.5cm (7 inches) including the finished floor, right?

Normally, the screed is planned to be 4.5cm (1.8 inches) above the heating pipes. This is generally seen as the minimum thickness. However, how should the maximum screed thickness be handled? Do you have any experience or recommendations regarding this, especially related to the heating system? At the spots with 19.8cm (7.8 inches), I would have to apply about 2cm (0.8 inches) more screed. That means it would be 4.5 + 2 + 2 (for the heating pipes) = 8.5cm (3.3 inches). Could this cause any problems? Vinyl flooring is planned as the final surface.

Additionally, I would like your advice on what you recommend for insulating the spaces above the supply and return pipes. Perlite? Our screed installer has suggested expanded clay aggregate with some added cement.
Mycraft13 Feb 2020 10:19
Cement Screed (CT)
Below are the thicknesses for floating screeds on insulation layers:

  • F4: Minimum nominal thickness up to or equal to 45 mm (1.8 inches), no maximum thickness
  • F5: Minimum nominal thickness up to or equal to 40 mm (1.6 inches), no maximum thickness
Subwkloofer16 Jul 2020 10:20
Is there a DIN standard where this can be looked up, or is it just a guideline?
T
Tamstar
16 Jul 2020 10:47
[LEFT]@Subwoofer
for example
DIN 18560
DIN 1264