ᐅ What installation spacing should be used for radiant floor cooling?

Created on: 19 Jan 2024 18:27
S
SandyBlack
Hello,

I am interested to know if any of you are using underfloor heating with a cooling function and have a pipe spacing greater than 10cm (5 inches).
What has your experience been like?
What pipe spacing do you typically use?

I would appreciate your comments.

Best regards
11ant20 Jan 2024 15:23
SandyBlack schrieb:

In your opinion, what are the catastrophic consequences of the planning? Apart from the higher supply temperature and thus lower efficiency?

Who was this follow-up question addressed to?
https://www.instagram.com/11antgmxde/
https://www.linkedin.com/company/bauen-jetzt/
H
Hausbau55EE
20 Jan 2024 15:29
SandyBlack schrieb:

What do you think are the disastrous consequences of the planning? Apart from the higher supply temperature and resulting lower efficiency?

@Hausbau55EE as I said, I’m aware of that. It’s miles away from Flow30. Still, investment costs must be included in the calculation. A heating system that is 10% more efficient doesn’t help me if the installation causes additional mid four-digit costs.


If you have no flexibility due to your construction contract with the general contractor, that’s unfortunate. Revising the plan towards Flow 30 might cost about 250 euros. Then a larger manifold with more heating circuits and labor and materials for tighter pipe spacing can be obtained from the heating installer at a low cost. Overall, I would estimate costs of a maximum of 1000 to 1500 euros. But the general contractor turns that into 4 or 5 thousand euros.
11ant20 Jan 2024 16:16
SandyBlack schrieb:

What do you think are the disastrous consequences of the planning? Apart from the higher supply temperature and thus lower efficiency?
Regarding question 2, I cannot agree with the higher supply temperature for cooling purposes. As for question 1, I seriously wonder, with great concern, how much of the general education common in "my time" must have been lost to even come up with such a plan without realizing what kind of substances inspired those ideas *shakes head*
https://www.instagram.com/11antgmxde/
https://www.linkedin.com/company/bauen-jetzt/
S
SandyBlack
20 Jan 2024 17:57
@Hausbau55EE The revision of the planning costs around 750 euros, regardless of the general contractor. But let’s assume the total additional costs are "only" 2,000 euros. It would still take between 10 and 20 years for these extra costs to pay off. And that does not include photovoltaics or the fact that you could invest the 2,000 euros now, which would significantly delay the payback period.

@11ant You mentioned the entire planning process, which also includes heating. Your other statement doesn’t help me much. Can you specifically describe what the catastrophic consequences of the planning are? I am fully aware that the planning has a lot of room for improvement. But this potential for improvement always points toward enabling lower supply temperatures for heating and possibly a somewhat better cooling effect. If you see any other disadvantages caused by this planning, I would appreciate it if you could explain them.
R
RotorMotor
20 Jan 2024 18:09
I have seen worse calculations before. The only obvious problem here is the bathroom.
Not just the pipe spacing, but especially the circuit length. Over 100 meters (330 feet) in the bathroom is really not good.
The 150W underperformance is already noted and is probably even higher in reality.
At least split that into two circuits. It only requires one additional valve.

How does it look in the shower/toilet room downstairs? That seems catastrophically short.
H
Hausbau55EE
20 Jan 2024 20:04
RotorMotor schrieb:

I’ve seen worse calculations. The only obvious disaster here is the bathroom.
It’s not just the pipe spacing but especially the circuit length. Over 100m (330 feet), especially in the bathroom, is really not good.
The 150W underperformance is already noted, and the actual value is probably even higher.
At least split this into two circuits. This only requires one extra valve.

How does it look in the shower/toilet room downstairs? That looks catastrophically short...


No heating load calculation is wasted... even if it only serves as a poor example in times like 2024.