How long would the experts here recommend making the individual heating circuits for the underfloor heating?
I need about 1350-1400 m (4400-4600 ft) total length. With 12 heating circuits, that still results in roughly 112 m (370 ft) per loop. Is that too long or acceptable?
Can anyone estimate the pressure loss over 112 m (370 ft) of 16x2 mm (5/8 x 1/16 inch) pipe?
I need about 1350-1400 m (4400-4600 ft) total length. With 12 heating circuits, that still results in roughly 112 m (370 ft) per loop. Is that too long or acceptable?
Can anyone estimate the pressure loss over 112 m (370 ft) of 16x2 mm (5/8 x 1/16 inch) pipe?
B
boxandroof11 Sep 2019 19:14I use 80m (260 feet) ±10% for all loops. Avoid especially long loops, particularly in rooms with high heating demand, such as bathrooms.
M
Michlhausbauaa24 Sep 2019 08:41Have a professional evaluate it.