M
M4rvin
Hi,
I wasn’t exactly sure which subforum to post in...

Our site manager asked us whether we want to place the bathtub directly on the screed or on the concrete slab. We hadn’t really thought about it until now, but we decided to go with the concrete floor.
Anyway, I was on site earlier and cut away the styrofoam, as the screed work is starting on Monday.

A few things caught my attention:

1) What should be the maximum spacing between the underfloor heating pipes? Some sections seem quite far apart, around 30cm (12 inches) to me.
2) Is it common to leave some areas without pipes? (Like the spot in front of the bathtub, see picture)
3) Now that I removed the styrofoam around the bathtub, there are still some pipes underneath. Don’t they cause any issues? And why is such unstable styrofoam even placed between the floor and the screed?

Thanks in advance
Marvin

Helle Schlauchbögen mit Kabelbindern auf blauer Rastermatte, dabei ein Maßband sichtbar.


Unterbodenheizungsrohre in Schleifen auf Dämmunterlage vor Fenster verlegt.


Badezimmer im Bau: blaue Wandabdichtung, gelbe Bodenrohre, Restfliesen und Bauplatten im Raum.
A
Alex124
24 Jun 2019 13:10
Bookstar schrieb:

Less than 10cm (4 inches) doesn't make sense, I would recommend 15cm (6 inches) for the bathroom and 20cm (8 inches) for the rest

Could I please have a technical explanation for this general statement?

I understand that it might be inconvenient for the installer to lay, but why exactly would it make no sense, especially for a heat pump where every degree of supply temperature is important?
G
guckuck2
24 Jun 2019 13:35
The statement by bookstar is simply incorrect.
Mycraft24 Jun 2019 14:25
This is what it looks like. General statements about underfloor heating are absolutely inappropriate, but for example, in the edge zones and especially in front of floor-to-ceiling windows, the loops are often installed with less than 10cm (4 inches) spacing because it makes a lot of sense to go below 10cm (4 inches) exactly in those areas.
A
Alex124
24 Jun 2019 14:35
Haha, thanks guys. I just wanted to give him a chance to correct that. It would be a shame if forum readers took it that way and applied it incorrectly.

Best regards from someone who installed their bathrooms themselves with a 5cm (2 inch) gap
T
Tego12
24 Jun 2019 21:20
The bathroom is almost always the critical room. A pipe spacing of 10 cm (4 inches) or less is practically always required, especially when using a heat pump (exceptions prove the rule).

If you also don’t want towel warmers, you almost always need an additional 1-2 walls with wall heating alongside the underfloor heating. That’s how we did it, and in my opinion, it’s the ideal solution, especially if the wall heating also includes the shower area.

All of this assumes you want an efficient heating system. You could also simply underspecify the system and raise the supply temperature arbitrarily. It will get warm, but that’s ecologically ineffective and financially unwise.
B
Bookstar
24 Jun 2019 22:19
I mentioned this because it makes more sense to increase the radiating surface, for example with wall heating. Installing it much thinner than 10 cm (5 inches) is often not possible due to the required bending radii.