we have been living in our newly built house (Efficiency House 55) since June 2021.
A hydraulic balancing was performed and adjusted accordingly by the plumbing company at the beginning of last week.
In the past few days, I have read up a bit on the topic and I think I have a reasonable understanding of the heat pump and underfloor heating system principle.
This morning I exported the data and hope you can give me helpful tips on how to reduce the heating a bit.
I also have the hydraulic balancing plan if that is important.
Thank you very much.
Heat Pump Commissioning
10/25/2021 06:58
Serial number 300415-193
KD index f
Serial number 2 300420-023
KD index 2 e
Serial number 3 000000-000
KD index 3 a
MAC 04-d1-6e-d0-1f-7c
IP 192.168.2.77
Subnet mask 255.255.255.0
Broadcast 192.168.2.255
Gateway 0.0.0.0
System status:
Heat pump type LD5
Software version V2.86.0
Bivalence level 1
Operating mode Domestic hot water
System settings:
Utility lockout without secondary heat
Room control station No
Integration separation unit
Mixing circuit 1 discharge
Mixing circuit 2 No
Mixing circuit 3 No
Secondary heat 1 type Electric heater
Secondary heat 1 function Heating and domestic hot water
Secondary heat 2 type No
Secondary heat 2 function No
Secondary heat 3 type No
Secondary heat 3 function No
Error without secondary heat
Domestic hot water sensor 1
Domestic hot water sensor 2 ZIP
Domestic hot water sensor 3 with ZUP
Domestic hot water sensor 4 target value
Domestic hot water sensor 5 without HUP
Domestic hot water + heat pump max 0.0 h
Pump optimization No
Service access Customer
Monitoring VD On
Control heating circuit outdoor-air-dependent
Control mixing circuit 1 outdoor-air-dependent
Control mixing circuit 2 outdoor-air-dependent
Control mixing circuit 3 outdoor-air-dependent
Boost heating with mixing
Electric anode No
Heating limit Yes
Parallel operation No
Remote maintenance No
Pump optimization time 180 min
Efficiency pump Yes
Heat quantity cooling circuit
Solar control temperature difference
Message TDI Yes
Multi-storage No
Release of secondary heat 60 min
Domestic hot water reheating No
Domestic hot water reheating max 5.0 h
Smart Grid No
Control mixing circuit 1 fast
Control mixing circuit 2 fast
Control mixing circuit 3 fast
Temperatures:
Return temperature limit 50.0°C (122°F)
Hysteresis HR 2.0 K
Temperature raise max 7.0 K
Release of secondary heat -5.0°C (23°F)
Air outlet temperature 7.0°C (45°F)
TDI target temperature 65.0°C (149°F)
Domestic hot water hysteresis 3.0 K
Outside temperature max 40.0°C (104°F)
Outside temperature min -20.0°C (-4°F)
End temperature LABT 6.0°C (43°F)
Setback down to -20.0°C (-4°F)
Max flow temperature 70.0°C (158°F)
Temperature difference on switch on 4.0 K
Temperature difference off 2.0 K
Temperature difference storage max 70.0°C (158°F)
TEE heating 2.0 K
TEE domestic hot water 5.0 K
Min. outdoor sensor flow max -7.0°C (19°F)
Flow ground floor 62.0°C (144°F)
Max domestic hot water temperature 65.0°C (149°F)
Min return target temperature 15.0°C (59°F)
Min flow mixing circuit 1 20.0°C (68°F)
Max flow mixing circuit 1 45.0°C (113°F)
Efficiency pump:
Efficiency pump nominal 8.25 V
Efficiency pump min 8.25 V
Efficiency pump Yes
Priorities:
Domestic hot water 1
Heating 2
System configuration:
Heating 1
Swimming pool 0
Heating curves heating 35.0°C (95°F)
Heating curves mixing circuit 1 35.0°C (95°F)
Operating time information:
Operating hours VD1 503 h
Compressor impulses 1 748
Average runtime VD1 00:40
Operating hours secondary heat 1 0 h
Operating hours heat pump 503 h
Operating hours heating 124 h
Operating hours domestic hot water 379 h
Temperature information:
Flow temperature 60.6°C (141°F)
Return temperature 57.2°C (135°F)
Return target 31.4°C (88°F)
External return 35.0°C (95°F)
Hot gas 91.0°C (196°F)
Outside temperature -0.5°C (31°F)
Average temperature 3.5°C (38°F)
Domestic hot water actual 57.9°C (136°F)
Domestic hot water target 60.0°C (140°F)
Heat source inlet 3.7°C (39°F)
Mixing circuit 1 flow 29.5°C (85°F)
Mixing circuit 1 flow target 31.4°C (88°F)
Solar collector 5.0°C (41°F)
Solar storage 150.0°C (302°F)
External energy source 5.0°C (41°F)
Compressor intake 3.0°C (37°F)
Evaporator intake -2.7°C (27°F)
Compressor heating 91.8°C (197°F)
Superheat 6.5 K
Superheat target 7.0 K
Yes = Yes
Shutdowns:
10/25/21 04:43 no error
10/25/21 03:33 no error
10/25/21 02:16 no error
10/25/21 01:10 no error
10/24/21 23:53 no error
Calibration:
NTC1 0.0
NTC2 0.0
NTC3 0.0
NTC4 0.0
NTC5 0.0
NTC6 0.0
NTC7 0.0
NTC8 0.0
10/25/2021 06:58
KD index f
KD index 2 e
KD index 3 a
IP 192.168.2.77
Gateway 0.0.0.0
System status:
Heat pump type LD5
Bivalence level 1
System settings:
Mixing circuit 2 No
Mixing circuit 3 No
Monitoring VD On
Electric anode No
Heating limit Yes
Efficiency pump Yes
Message TDI Yes
Multi-storage No
Smart Grid No
Temperatures:
Hysteresis HR 2.0 K
TEE heating 2.0 K
Efficiency pump:
Efficiency pump Yes
Priorities:
Heating 2
Heating 1
Swimming pool 0
Superheat 6.5 K
Yes = Yes
Shutdowns:
Calibration:
NTC1 0.0
NTC2 0.0
NTC3 0.0
NTC4 0.0
NTC5 0.0
NTC6 0.0
NTC7 0.0
NTC8 0.0
Set your forward temperature to 32°C (90°F) instead of 45°C (113°F) initially, as 45°C is too high for a heat pump. It should get cooler this way. Monitor the system for a few days to see if this setting is appropriate. If it gets too cold, increase the temperature slightly, but only in 1-2°C (2-4°F) increments, and always wait 2-3 days for the system to stabilize before making further adjustments.