ᐅ Please review my mechanical ventilation system design for residential buildings.

Created on: 21 Feb 2019 09:50
C
Christian NW
2D floor plan of a house with room layout and building service diagram on the right

Floor plan of a house with red heating installation and yellow sanitary pipes, building services layout

2D floor plan of a house with breakthrough planning in the attic


Hello everyone,

could you please review my mechanical ventilation with heat recovery (MVHR) system design?

Objectives:
1. Good air quality in all rooms
2. A system that is absolutely quiet and hardly audible in the rooms

Questions:
1. Are the airflow rates sufficient?
2. Is the system barely audible?
3. ...

Thanks in advance!!

Attached are the planning documents.

We are using the RecoVair 360/4 from Vaillant.
HIGIL27 May 2019 14:45
Hello Christian,

In my opinion, floor-level outlets are not recommended. They cause dust convection, and the air entering the house is always a few degrees cooler than the existing air, so it immediately sinks. A ceiling diffuser or a wall vent placed in the upper third of the room would be better. The requirement is 45 m³/h (approximately 26.5 CFM) for both kitchen and bathroom. So, with a 75 mm (3 inch) flexible duct, you need to use two ducts leading to one vent to keep the air velocity below 2.5 m/s (about 8.2 ft/s) and thus avoid drafts.

Alternatively, and even better, install two exhaust vents per exhaust room, each connected to a single duct. This would also ensure better distribution of the exhaust air within the room.

I also notice the absence of a sound attenuator in the exhaust air duct to the wall.

As a recommendation, never design for more than 30 m³/h (about 17.6 CFM) per 75 mm (3 inch) flexible duct.

My device recommendation is exclusively rotary heat exchangers.

Advantages:
Moisture recovery, no system-related electric preheating needed in winter, no condensate, and pollen filter as standard from the factory.

Best regards,
HIGIL