ᐅ KfW40 house offer with heat pump and mechanical ventilation with heat recovery— is it worth it?

Created on: 25 May 2019 21:19
Q
querys_
Hello everyone,
Today I received a house offer from a prefabricated house supplier.
They list the exhaust air heat pump Nibe F 750 with supply air module SAM 40 as the heating system. The maximum building heating load is said to be 7.5 kW.
Additionally, there is underfloor heating and a 180 L (48 gallon) domestic hot water storage tank.
The house is located near Cologne/Bonn Airport (for climate reference) and is about 120 m² (1,290 sq ft) in size (excluding the basement).

I have already read a lot of negative things about exhaust air heat pumps, so I want to ask again if this system is any good, and if not, what would be an alternative and how much more would that cost?

Thank you very much!
B
boxandroof
27 May 2019 11:23
The Geothermie-NRW links are not related to the slinky trench collector, so I would not rule it out yet.
G
guckuck2
27 May 2019 12:06
Lumpi_LE schrieb:

What kind of house is that supposed to be?
I find that quite unrealistic.

This is a reasonable target value for building a KfW 40 house.
For example, a timber frame construction can achieve this quite easily.
Alternatively, a calcium silicate brick wall with 200mm (8 inches) of EPS insulation with a thermal conductivity of 0.032 W/(m·K) applied can also reach this range.

Monolithic construction methods, however, have difficulties meeting such requirements.
L
Lumpi_LE
27 May 2019 12:19
Please show me a KfW-40 house with a heating transmission coefficient (HT') of 0.14.

There is no doubt that it is possible, but a KfW-40 house from a prefabricated house manufacturer, as TE described, will never achieve this value.

It simply cannot be done with a timber frame construction, unless you eliminate the supply temperature at the windows. It also cannot be achieved with sand-lime brick and 200mm (8 inches) insulation.

Edit: Supply temperature for better understanding: We have about 20m² (215 sq ft) of windows and 160m² (1722 sq ft) of walls. The windows have a Uw value of 0.8. To compensate the windows with the walls and reach an HT' of 0.14, the walls would need a U value of about 0.06. That corresponds to roughly 60cm (24 inches) of insulation. And that does not even account for thermal bridges.
Q
querys_
27 May 2019 12:58
@Lumpi_LE Thanks for the overview. I only mentioned gas for comparison. Actually, I don’t want to have gas connected to the house, so in the end, I can also save the connection costs.
G
guckuck2
27 May 2019 17:19
Lumpi_LE schrieb:

Please show me a KfW-40 house with a heat transfer coefficient (HT') of 0.14.
There is no doubt it’s possible, but a KfW-40 house from a prefab home provider as TE describes will never achieve this value.

It’s simply not possible with a timber frame, unless you omit the supply temperature to the windows. It’s just as impossible with calcium silicate blocks and 200mm (8 inches) of insulation.

Edit: To clarify supply temperature: We have about 20m² (215 sq ft) of windows and 160m² (1,722 sq ft) of walls. The windows have a Uw-value of 0.8. If I wanted to compensate for the windows with the walls to reach an HT' of 0.14, the walls would need a U-value of about 0.06. That means roughly 60cm (24 inches) of insulation. And that still doesn’t account for thermal bridges.

Everything is correct, but it’s off-topic here.
He received the U-values of individual components from his home provider. He is using them for the calculator because he has no other data. At this point, that is the only reasonable approach.
L
Lumpi_LE
27 May 2019 20:31
A completely nonsensical approach. If I want to know how many liters my car consumes per 100 km (62 miles) and someone tells me that the tank holds 60 liters (16 gallons), I obviously wouldn't assume 60 liters per 100 km.
But anyway, he already understood that and calculated with a heat transfer coefficient of 0.3.