ᐅ Connection of IKEA FRAMTID HGC4T and IKEA FRAMTID OV5 possible
Created on: 1 Feb 2011 14:40
S
SolourHello,
we want to connect the Framtid HGC4T and FRAMTID OV5.
According to my calculations, the consumption could be up to 6.5 kW or 1 kW.
Converted (at 220-400 V or 230 V): this means 16.5 A to 29.5 A and 4.4 A.
However, the stove connection outlet is only rated for 26 A.
Can I connect the cooktop and the oven together?
Or would it be better to connect the cooktop to the stove connection outlet and the oven, washing machine, and dishwasher to a standard 16 A outlet?
Is my rough calculation completely wrong?
What do you think?
Best regards
S
P.S.: (Of course, I won’t be connecting anything myself, but where and how it should be connected needs to be clarified in advance...)
we want to connect the Framtid HGC4T and FRAMTID OV5.
According to my calculations, the consumption could be up to 6.5 kW or 1 kW.
Converted (at 220-400 V or 230 V): this means 16.5 A to 29.5 A and 4.4 A.
However, the stove connection outlet is only rated for 26 A.
Can I connect the cooktop and the oven together?
Or would it be better to connect the cooktop to the stove connection outlet and the oven, washing machine, and dishwasher to a standard 16 A outlet?
Is my rough calculation completely wrong?
What do you think?
Best regards
S
P.S.: (Of course, I won’t be connecting anything myself, but where and how it should be connected needs to be clarified in advance...)
M
Maverick18542 Feb 2011 09:081.
Do you always keep your cooktop on the highest setting and the oven at full power?
2.
Is the house an older building? Then it’s possible that you have a weaker electrical circuit. Newer homes typically have three 16 ampere breakers installed as standard.
But please make sure to have the connection done by a qualified electrician. They should know what they’re doing.
Do you always keep your cooktop on the highest setting and the oven at full power?
2.
Is the house an older building? Then it’s possible that you have a weaker electrical circuit. Newer homes typically have three 16 ampere breakers installed as standard.
But please make sure to have the connection done by a qualified electrician. They should know what they’re doing.