ᐅ Guntamatic Pellet Heating System: Supply Water Temperature Too High

Created on: 22 Dec 2018 19:03
E
Earth2018
Earth201822 Dec 2018 19:03
Hello everyone,
apparently my pellet boiler is set up incorrectly. I’ve tried and checked quite a few things but can’t figure it out. The supply temperature goes above 50°C (122°F). I’m worried my floor tiles might crack 😉 (underfloor heating).

It’s a Guntamatic with 10 kW.

What I’ve already checked:
- Mode is Eco-Ideal, which should be correct
- Operation mode is Normal
- Temporary setpoint temperature at 18°C (64°F) made no difference in lowering the supply temperature
- Heating curve was adjusted from 0.6 to 0.5 (0.6 should be fine)
- Screed heating is of course switched off
- Max supply temperature is set to 37°C (99°F), so it should never get that hot...

Attached are some pictures:

Anzeige eines Heizkessel-Status mit Temperatur, Leistung und Außentemperatur


Infodisplay zeigt Kesselparameter wie Abgastemperatur, CO2-Gehalt und Wirkungsgrad.


Display eines Haustechnik- und Heizungssteuergeräts mit Warmwasseranzeige


Heizungssteuerungsdisplay mit Pumpensteuerung, Uhrprogramm und Solltemperaturen


Bedienfeld einer Heizungsanlage mit Puffer-Speicher und Temperaturanzeigen


Digitale Heizungssteuerung auf Display mit Einstellungen für Heizkreis HK1, Mischerlauf und Vorlaufparameter


Digitales Heizungssteuerungsdisplay mit HK1-Einstellungen, Estrichheizen und Freigabe


Zwei Druckmessgeräte an isolierten Heizungsrohren mit Thermostat unten
wrobel22 Dec 2018 19:20
Hello

Is the boiler connected to a buffer tank? From the buffer tank, does it go through a mixing valve and mixing valve motor?
Is the mixing valve operating correctly, or is it possibly set to manual mode?

Olli
Earth201822 Dec 2018 19:28
Hello Oli,
Yes, I have a mixer; at least it was still functioning yesterday.

In the picture, you can see the mixer. It is set to the lowest setting. Does that mean it adds only a little heat, or a lot?

Regarding your other questions, I find it difficult as a layperson, but I’ll try to explain. You will understand what I mean 😉

The pellet heating system heats the large buffer tank responsible for the domestic hot water. The underfloor heating line runs through this buffer tank 😉 What do you mean by boiler? The large buffer tank, I suppose.

To my (layperson’s) knowledge, I don’t have a buffer tank specifically for the underfloor heating.

Building services pipes with pressure regulator and pressure gauge in the technical room
wrobel23 Dec 2018 00:18
Hello
Based on the position of the mixing valve actuator, almost exclusively water from the return line should flow into the supply line.
First, check whether the mixing valve actuator is mounted correctly on the valve.
You can also try pressing the round button and then turning it fully to the right.
Does the supply temperature drop then?


Olli
Earth201825 Dec 2018 13:23
So, the mixer doesn't move. I opened it up earlier and noticed that the screw holding the "knob" is loose. I've just read that you also need to push in to adjust it manually. I'll try that again later.

Apparently, it wants to take the water from the return line (to reduce the flow) but can't, maybe because the component is not seated correctly.

I'll take another look at it later. I currently live about half an hour away...
Earth201826 Dec 2018 16:29
Should the red ring be visible when the system is regulating? Or should I press it in?

Black shut-off valve knob with red ring on pipe connection in building services