Tobias Oelrich14 Feb 2021 18:08Hello, we received the information about our heating system for the new build (120 sqm (1,292 sq ft) living area) yesterday.
I would like to hear your opinions about it.
Nothing has been installed yet ;-)
I would like to hear your opinions about it.
Nothing has been installed yet ;-)
T
Tobias Oelrich14 Feb 2021 18:51What am I supposed to tell him, don’t they know best?
I have read that with proper installation it can even provide cooling.
What should you pay attention to in this case?
I have read that with proper installation it can even provide cooling.
What should you pay attention to in this case?
T
T_im_Norden15 Feb 2021 06:45Heat pump matched to heating load
Supply temperature not higher than 30 degrees Celsius (86°F)
Room-by-room heating load calculation according to DIN standard
Specify the desired temperature for each room; otherwise, 20 degrees Celsius (68°F) for rooms and 24 degrees Celsius (75°F) for bathrooms will be used by default.
Install underfloor heating beneath bathtubs and showers.
Consider installing wall heating in bathrooms (underfloor heating integrated into the wall).
Pipe diameter at least 17 x 2 mm (approx. 0.67 x 0.08 inches) for distribution pipes.
All heating circuits should be roughly the same length, none longer than 100 meters (330 feet).
Connect the heating circuit manifold (HKV) with sufficiently large pipe diameters.
Avoid pipe crimp connections where possible.
Have the underfloor heating design calculated by an external specialist firm; it costs a few hundred euros but is well worth it.
See the discussion thread by Tolentio and OWL.
Supply temperature not higher than 30 degrees Celsius (86°F)
Room-by-room heating load calculation according to DIN standard
Specify the desired temperature for each room; otherwise, 20 degrees Celsius (68°F) for rooms and 24 degrees Celsius (75°F) for bathrooms will be used by default.
Install underfloor heating beneath bathtubs and showers.
Consider installing wall heating in bathrooms (underfloor heating integrated into the wall).
Pipe diameter at least 17 x 2 mm (approx. 0.67 x 0.08 inches) for distribution pipes.
All heating circuits should be roughly the same length, none longer than 100 meters (330 feet).
Connect the heating circuit manifold (HKV) with sufficiently large pipe diameters.
Avoid pipe crimp connections where possible.
Have the underfloor heating design calculated by an external specialist firm; it costs a few hundred euros but is well worth it.
See the discussion thread by Tolentio and OWL.