ᐅ Excavation/Foundation Construction in High Groundwater Areas – Experiences?

Created on: 19 Mar 2024 12:01
G
gregman22
Dear community,

We are facing a challenge as our earthworks were actually supposed to start since this/last week. However, our plot is located in a high groundwater area, and the earthworks are complicating things. I haven’t received clear statements from our earthworks contractor, so I would like to hear about your experiences.

Situation:
- Basement floor slab with overhangs needs to be poured
- Groundwater is currently about 1.85 m (6 feet) below the plot surface
- Excavation for the basement floor slab must reach 3.55 m (12 feet) deep → thus, the earthworks will be 1.70 m (5.5 feet) below the groundwater level
- Planned earthworks measures: 3 boreholes for dewatering; pipeline route to sewer 470 m (1,540 feet), diameter of sewer pipe into which we can discharge: 40 cm (16 inches)
- Additionally: We have installed a soakaway well on the property, reaching a depth of 8 m (26 feet), theoretically allowing further water discharge
- Weather forecast for the next two weeks looks rather positive (2-3 rainy days, otherwise mostly dry); on dry days, the water level drops about 1-2 cm (0.4–0.8 inches) per day

Further info: At the very beginning, sheet piling was considered. However, no clear necessity was explained to me, so I decided against it—mainly due to the risks of damaging neighboring houses.

Currently, our earthworks contractor is installing the pipes and planned to start pumping from Friday.

Now my main question to you: How do you see the situation? How optimistic can I be that it will work out, on a scale from 0 (very pessimistic) to 10 (very optimistic)?

Thank you all.

Best regards
A
Allthewayup
20 Mar 2024 17:29
When should the pumping start?
G
gregman22
20 Mar 2024 17:30
Originally, the plan was to start the day after tomorrow (March 22); excavation would begin next week; followed immediately by basement construction starting April 3.

New plan: pumping starts on March 27 -> basement construction begins April 9.
A
Allthewayup
20 Mar 2024 17:34
I reviewed your table again. I noticed that it only covers data from shallow depths. Does the soil report explicitly include a chapter on groundwater lowering or construction dewatering? I was ultimately unable to make much use of the data from the table.
G
gregman22
20 Mar 2024 17:51
Here are a few screenshots 🙂 This should provide more context.
Groundwater conditions: KB1/KB2; GW 1.85/1.80 m (6.1/5.9 ft) below ground level; groundwater elevation 515.31/515.24 m (1690.4/1689.7 ft) above sea level

Protection of buildings against groundwater and seepage water; design water level 516.80 m (1695.6 ft) above sea level.

Borehole profile with yellow sediment layer; gravel, sandy, silty; depth scale 1:50.

Borehole profile with gravel, sand, and silt layers; elevation above sea level 509.16–517.16 m (1670.0–1697.0 ft), scale 1:50.

Technical text about permeable gravel-sand mixture, infiltration, ATV A 138 standard, design value 1e-4 m/s.

Document page, section 6.6 Infiltration: text about infiltration of roof runoff water.

Page from a technical document on construction dewatering, excavation slope stability, and shoring.
A
Allthewayup
20 Mar 2024 19:19
Finally some useful information!
So, you have soil class GU, which we had as well—that’s good. I would therefore disregard any concerns about subsidence damage to neighboring buildings. Strongly sandy soils tend to shrink when they lose water; for example, look at the surface of dried-up lakes, where a cracked landscape remains. This doesn’t happen if (fine) gravel dries out.
30 liters per second (l/s) is quite substantial. That converts to 2,592,000 liters per 24 hours.
We didn’t even pump a third of that amount.

However, we also didn’t reach the volume I initially calculated but ended up below it. This is simply due to the calculation formula behind that figure, which assumes a linear inflow into the excavation pit. But since a drawdown cone forms around the pump shaft, this water volume decreases noticeably day by day. With today’s knowledge, I would estimate about half of that amount. At first, you’ll even pump more than 30 l/s. On day 7, for example, it might be “only” 18 l/s, and ten days later perhaps just 10 l/s. The pumps ran 24/7 for the first three days and then started switching off more and more frequently—sometimes for up to 30 minutes. Then they’d pump for 5 minutes, and so on.
A
Allthewayup
20 Mar 2024 19:27
Excavation pit with orange brick walls, red scaffolding, foundation slab, and concrete floor.

View inside a round shaft; a rope or cable leads to the center of the dark interior.


This is what one of the two pump shafts at our site looked like. They are concrete rings with holes. The rings had a diameter of 100cm (39 inches).