ᐅ Mechanical Ventilation with Heat Recovery – You Can Hear Every Word from Another Room – Is This Normal?

Created on: 30 Jul 2018 22:43
D
Dodo86
Hello everyone,
We had the final inspection of our house two weeks ago. Now we have noticed that through the central ventilation system in the guest bathroom and utility room, every word spoken in the dining/kitchen/living area can be heard very clearly, as if you were sitting right next to each other. With the bathroom door open, the sound naturally carries up to the children’s bedrooms upstairs. On the upper floor, the sound transmission through the controlled mechanical ventilation system is significantly less.
Can I still report this as a defect after the final inspection?
Thank you very much and best regards!
C
Curly
1 Aug 2018 09:45
Dodo86 schrieb:
Did you have to purchase the sound dampers separately, or are they usually included?

Everything was included for us.

Best regards
Sabine
Dodo861 Aug 2018 11:16
First of all, thanks for all the replies. Yes, it really is strange. But the noise definitely comes through the ducts.
It is very loud through the exhaust vent, every word audible. Even in the upstairs bathroom it's still clearly heard. The supply air carries the sound muffled. But of course, it's quite annoying when the children's rooms are not quiet. And the humming of the ventilation system is also transmitted from the utility room into all other rooms.
Here are some photos: the first one shows the exhaust vent in the kitchen. The others are from the utility room.

Modern kitchen with dark cabinets and two built-in ovens; visible wiring on the ceiling.


Basement room with building services: insulated air ducts, pipes, and distribution cabinet.


Metal air duct with perforated cover above wooden furniture in basement room


Basement room with visible stainless steel ventilation ducts, piping and washing machine


HVAC system with insulated ventilation ducts in the technical room
Dodo861 Aug 2018 11:23
Here are two pictures from the utility room showing the pipe from the kitchen splitting and leading once to the guest bathroom and once to the appliance.

Mehrere Metall-Lüftungsrohre und Kanäle in einem Technikraum


Kellerraum mit Heizungs- und Lüftungsleitungen und isolierten Luftkanälen.


Metallische Lüftungsrohre und Rohrleitungen im Haustechnikraum.
Mycraft1 Aug 2018 13:06
Ah, okay, you chose the "series connection" option. Yes, in this case, sound can be transmitted very effectively.

Telephone line dampers between the rooms are necessary.

I would ask whether anything like that has been installed.
A
Alex85
1 Aug 2018 13:26
The exposed metal pipe alone conducts a significant amount. In the commonly used systems here, the plastic is embedded in concrete or under the screed.

I believe the flexible ducts at the unit have sound-dampening properties, but as mycraft mentioned, that is probably not enough.
Dodo861 Aug 2018 13:54
Someone from the contracting company is coming by tomorrow.
Is it standard practice to install the sound dampers?
No one ever informed us that this could happen, and the company representatives even said on the phone that it couldn’t be the case... Is it possible to retrofit these sound dampers without any issues?