ᐅ Mechanical ventilation with heat recovery: no – explanation provided in the text.
Created on: 15 Jul 2015 00:00
G
Grym
For a long time, I was very much in favor of controlled residential ventilation, but I have now revised my opinion. First, some basic considerations:
- Modern houses are built so tightly that additional mechanical ventilation is necessary; otherwise, windows must be opened several times a day, summer and winter, for airing out
- Whether this ventilation is manual or automatic is a matter of comfort
- Whether this ventilation includes heat recovery or not is a question of economic efficiency
When considering economic efficiency, cleaning costs must be included. A reputable provider who only sells controlled residential ventilation estimated these costs at 700 EUR, with a recommended cleaning interval of at least every 5 years. However, in the demonstration house, the first cleaning was done after only 2 years because a microbial test detected contamination in the supply air exceeding the limit values (I don’t know the exact limits, but if the seller says cleaning after 2 years was necessary, I take their word for it—the company does not sell a house without controlled residential ventilation).
Depending on whether you divide the 700 EUR over 5 years or 2 years, the annual maintenance costs come to between 140 and 350 EUR.
The unit itself consumes electrical energy, approximately 250–400 kWh_el per year, which costs between 63 and 100 EUR annually.
The controlled residential ventilation system is a technical device; assuming a service life of 15 years, removal and disposal of the old unit, a new unit, and commissioning are estimated at around 5,000 EUR. This results in an annual depreciation of 333 EUR. If the ventilation system is expected to last 20 years, with disposal, new unit, and commissioning costs totaling 4,000 EUR, then depreciation is 200 EUR per year.
For new filters, maintenance, and minor repairs, I estimate a flat rate of 100 EUR.
Total annual costs in the best case scenario: 140 + 63 + 200 + 100 = 503 EUR
Total annual costs in the worst case scenario: 350 + 100 + 333 + 100 = 883 EUR
The savings effect is roughly estimated at about 2,000 kWh_thermal up to over 3,000 kWh_thermal. 2,000 kWh_thermal equate to 2,000 kWh of gas at 5.5 cents or 400–500 kWh_el at 20 cents (heat pump tariff) or 25 cents (household electricity). This results in savings of about 110 EUR (gas), 125 EUR (air-source heat pump with household electricity), or 80 EUR (ground-source heat pump with heat pump electricity).
At 3,500 EUR savings, this corresponds to 193 EUR (gas), 219 EUR (worst-case heat pump), or 140 EUR (best-case heat pump).
If you compare the best-case controlled ventilation with the worst-case heat pump, you get 503 EUR - 219 EUR = 284 EUR. The other way around is 883 EUR - 140 EUR = 743 EUR.
No matter how you look at it, controlled ventilation with heat recovery cannot even save the running costs. Therefore, in my opinion, the best system—especially to avoid hygienic problems in the house—is exhaust air modules in wet rooms combined with window rebate ventilation or an external wall air inlet. Decentralized controlled ventilation systems with heat recovery do not have such high cleaning costs, but even they would never recoup the additional cost of heat recovery. Additionally, these devices must be placed in bedrooms and living areas, which creates noise. Pure exhaust air systems without heat recovery are suitable in rooms where quiet noises are less disturbing (kitchens, toilets, utility rooms, bathrooms) and can even be switched off for hours (bathroom). Modern window rebates work without drafts and reduce sound insulation by only 1 to 2 dB. Anyone living in a quiet residential area probably doesn’t mind.
I look forward to the discussion, but please keep it relevant to the topic. I am not questioning the necessity of non-user-dependent mechanical ventilation; my focus is only on central heat recovery. Central heat recovery requires the duct system, which incurs high cleaning costs, as well as a complex technical device with limited service life and high costs (unlike a standard exhaust air module without heat recovery). Controlled ventilation without heat recovery operates without the duct system.
- Modern houses are built so tightly that additional mechanical ventilation is necessary; otherwise, windows must be opened several times a day, summer and winter, for airing out
- Whether this ventilation is manual or automatic is a matter of comfort
- Whether this ventilation includes heat recovery or not is a question of economic efficiency
When considering economic efficiency, cleaning costs must be included. A reputable provider who only sells controlled residential ventilation estimated these costs at 700 EUR, with a recommended cleaning interval of at least every 5 years. However, in the demonstration house, the first cleaning was done after only 2 years because a microbial test detected contamination in the supply air exceeding the limit values (I don’t know the exact limits, but if the seller says cleaning after 2 years was necessary, I take their word for it—the company does not sell a house without controlled residential ventilation).
Depending on whether you divide the 700 EUR over 5 years or 2 years, the annual maintenance costs come to between 140 and 350 EUR.
The unit itself consumes electrical energy, approximately 250–400 kWh_el per year, which costs between 63 and 100 EUR annually.
The controlled residential ventilation system is a technical device; assuming a service life of 15 years, removal and disposal of the old unit, a new unit, and commissioning are estimated at around 5,000 EUR. This results in an annual depreciation of 333 EUR. If the ventilation system is expected to last 20 years, with disposal, new unit, and commissioning costs totaling 4,000 EUR, then depreciation is 200 EUR per year.
For new filters, maintenance, and minor repairs, I estimate a flat rate of 100 EUR.
Total annual costs in the best case scenario: 140 + 63 + 200 + 100 = 503 EUR
Total annual costs in the worst case scenario: 350 + 100 + 333 + 100 = 883 EUR
The savings effect is roughly estimated at about 2,000 kWh_thermal up to over 3,000 kWh_thermal. 2,000 kWh_thermal equate to 2,000 kWh of gas at 5.5 cents or 400–500 kWh_el at 20 cents (heat pump tariff) or 25 cents (household electricity). This results in savings of about 110 EUR (gas), 125 EUR (air-source heat pump with household electricity), or 80 EUR (ground-source heat pump with heat pump electricity).
At 3,500 EUR savings, this corresponds to 193 EUR (gas), 219 EUR (worst-case heat pump), or 140 EUR (best-case heat pump).
If you compare the best-case controlled ventilation with the worst-case heat pump, you get 503 EUR - 219 EUR = 284 EUR. The other way around is 883 EUR - 140 EUR = 743 EUR.
No matter how you look at it, controlled ventilation with heat recovery cannot even save the running costs. Therefore, in my opinion, the best system—especially to avoid hygienic problems in the house—is exhaust air modules in wet rooms combined with window rebate ventilation or an external wall air inlet. Decentralized controlled ventilation systems with heat recovery do not have such high cleaning costs, but even they would never recoup the additional cost of heat recovery. Additionally, these devices must be placed in bedrooms and living areas, which creates noise. Pure exhaust air systems without heat recovery are suitable in rooms where quiet noises are less disturbing (kitchens, toilets, utility rooms, bathrooms) and can even be switched off for hours (bathroom). Modern window rebates work without drafts and reduce sound insulation by only 1 to 2 dB. Anyone living in a quiet residential area probably doesn’t mind.
I look forward to the discussion, but please keep it relevant to the topic. I am not questioning the necessity of non-user-dependent mechanical ventilation; my focus is only on central heat recovery. Central heat recovery requires the duct system, which incurs high cleaning costs, as well as a complex technical device with limited service life and high costs (unlike a standard exhaust air module without heat recovery). Controlled ventilation without heat recovery operates without the duct system.
Germ measurement after 2 years: Above-average levels of germs. Even if acceptable, cleaning is recommended at the latest after 5 years. These are the facts.
I would not overestimate the filter. The coarse filter helps against insects and larger debris, while the pollen filter is designed for pollen. I am quite certain that germs can pass through freely, and I am absolutely sure that fine dust passes through without any restriction. Effective filtration of PM10 or even PM2.5 requires completely different filters.
I would not overestimate the filter. The coarse filter helps against insects and larger debris, while the pollen filter is designed for pollen. I am quite certain that germs can pass through freely, and I am absolutely sure that fine dust passes through without any restriction. Effective filtration of PM10 or even PM2.5 requires completely different filters.
S
Sebastian7915 Jul 2015 09:15Yes, the dangerous "germs" – as I said, just bury yourself and better stop breathing. What nonsense...
Maybe your experts should define what these germs actually are.
And stop with your "facts" – your blunt statements don’t prove any expertise. Those are not facts...
Maybe your experts should define what these germs actually are.
And stop with your "facts" – your blunt statements don’t prove any expertise. Those are not facts...
There is a difference between inhaling low concentrations of microbes from general outdoor air and having them accumulate over time in a controlled residential ventilation system. You seem to be resistant to any kind of facts, don’t you? Most systems run for 5 to 10 years or longer because most people simply don’t care. It’s not like you can see the microbial contamination. The fact is, for a system installed in 2011 or 2012, a microbial test was conducted after 2 years. Homeowners normally don’t do this, but the company can afford it. The result was: contaminated. Fact list complete.
S
Sebastian7915 Jul 2015 09:21Yes, then we ventilation system users all live with germs - good that you are so forward-thinking.
Apparently watched too much Pippi Longstocking...
Apparently watched too much Pippi Longstocking...
S
Sebastian7915 Jul 2015 09:42I installed it myself, and the planning and delivery of the parts were handled by Lüftung.net (no link, that’s the company name) – so far, I am very satisfied. The price-performance ratio for self-installation is unbeatable compared to quotes from companies.
I had previously tried selfio, but I was mainly not satisfied with their calculation of the air ducts and the type/number of outlets. With Lüftung.net, I was presented with a much better ventilation concept and everything was clearly explained – why, how, and what!
I had previously tried selfio, but I was mainly not satisfied with their calculation of the air ducts and the type/number of outlets. With Lüftung.net, I was presented with a much better ventilation concept and everything was clearly explained – why, how, and what!