ᐅ Temporary construction power: What type of cable is sufficient?

Created on: 10 Mar 2022 20:33
B
Bauenaberwie
Hello,

we need to cover a distance of 40-50m (131-164 feet) to reach our plot. An early temporary power connection is not feasible timing-wise, so we have to pull a cable. Now I am wondering whether 5x16mm² (5x0.63 inch²) is sufficient or if it must be 5x25mm² (5x0.98 inch²). I have browsed various sites but am still not quite sure.

For construction, we require 1x63A and 2x32A.

Thank you very much
B
Bauenaberwie
11 Mar 2022 09:29
Ok, perfect, thank you very much!
Characters characters!
Nida35a11 Mar 2022 09:43
PhiIipp schrieb:

And
The cable has been laid to the house for 3 years,
the person doing the calculations is not just an office worker, and the total maximum load was considered at 70%.
There are increasingly more devices that react to voltage drop by switching off.
PhiIipp11 Mar 2022 10:05
Nida35a schrieb:

The cable has been running to the house for 3 years,
the person who did the calculations is not just an office worker, and the total maximum load was estimated at 70%.
There are more and more devices that shut off when they detect a voltage drop.

I wasn’t aware that household appliances have undervoltage protection triggers. A quick search didn’t find anything on that.
And you won’t reach 70% of the rated load during hundreds of cold winters.
With a 50 mm² (0.0775 in²) main supply cable, you can deliver about 160 A / 50 kVA to the house. That is oversized by a factor of 3 for a single-family home.
The voltage drop is completely negligible, especially since utility companies nowadays tend to operate at a higher network voltage around 235 V (235 V).

I stand by my opinion. Your consultant meant well, but your supply line is massively oversized.