Hello,
today I found an offer from the local grid operator in my mailbox – a new grid connection contract for just under 3,000€.
I looked it up and the Federal Network Agency states:
Now, I calculate it – the contract specifies a main fuse for the house connection of 3 x 63 amperes. At 400 volts per phase (correct, right?), that equals 75.6 kW?! The provider tells me this is a completely normal residential connection that always costs money.
So why does the Federal Network Agency say the above? Wikipedia says 30 kW is enough for four housing units... we are building a small single-family house.
Thanks 🙂
today I found an offer from the local grid operator in my mailbox – a new grid connection contract for just under 3,000€.
I looked it up and the Federal Network Agency states:
A construction cost contribution may only be charged for the portion of the power demand that exceeds 30 kilowatts. Therefore, the standard residential electricity connection is exempt from construction cost contributions.
Now, I calculate it – the contract specifies a main fuse for the house connection of 3 x 63 amperes. At 400 volts per phase (correct, right?), that equals 75.6 kW?! The provider tells me this is a completely normal residential connection that always costs money.
So why does the Federal Network Agency say the above? Wikipedia says 30 kW is enough for four housing units... we are building a small single-family house.
Thanks 🙂
K
Knallkörper8 May 2017 17:42Are construction cost subsidies included in the 3000 euros (approximately 3200 USD)?
C
Caspar20208 May 2017 17:55The construction cost subsidy is not the expense for connecting the house to the street; rather, it is a grant to build or expand the downstream infrastructure according to the load requirements.
These are two completely different things.
And in my opinion, the formula is also incorrect.
P = U * I * √3 * cosφ
This is three-phase power, not three times direct current.
These are two completely different things.
And in my opinion, the formula is also incorrect.
P = U * I * √3 * cosφ
This is three-phase power, not three times direct current.
K
Knallkörper8 May 2017 18:05The formula is correct, but it is 230V per phase.