ᐅ Black engobed roof tiles / Faster intense heating / Upper floor?
Created on: 13 May 2013 09:25
Philiboy83
we went out over the weekend to choose roof tiles, and we like a roof tile from Creaton (type Balance) in the color Nuance black engobed. However, I’m not sure if the tile is only engobed or also glazed, as it has a refined silky sheen in the engobe coating.
But what about heat in the summer? Does this type of tile transfer heat to the insulation faster than, for example, a red tile? A sunny weekend doesn’t really matter, but it becomes more interesting during a longer heatwave. If the heat penetration is only delayed by about one day with a red tile, then it probably doesn’t make much difference either.
Our upper floor construction from inside to outside is as follows: 12.5 mm (1/2 inch) drywall, 15 mm (5/8 inch) OSB, 240 mm (9.5 inches) 035 glass wool insulation between the rafters. On top of that is DeltaMaxx foil (or something similar) and then the roof covering.
Bauqualle
12 Jun 2013 10:39
Philiboy83 schrieb:
But what about the issue of heat in summer?
.. then please create a long-term table showing when it is actually extremely hot in Germany and when we have mild and cold days here in Germany ...
TomTom1
12 Jun 2013 19:17
K.Brodbeck schrieb:
Hello Philiboy83,
I also think that the color of the brick is of secondary importance.
Mineral wool insulation has low thermal mass, which means it transfers heat relatively quickly. Cellulose and/or soft fiber boards have significantly higher thermal mass. This means the living space behind them heats up more slowly. This is what is meant by summer thermal protection.
If something hinders cooling down, there is a simple solution: ventilation! Here in Konstanz, a lot of potential heat loss is wasted in an unoccupied attic space.
K.Brodbeck
Hello!
Interesting connection – but probably incorrect. Thermal mass is a matter of mass. A lot of mass stores a lot of heat – it’s a different matter when it comes to heat transfer. Try holding a (high-mass) metal rod in a campfire.
Vacuum insulation panels tend not to conduct heat, but they also do not store it.
Regarding ventilation: The old apartment was right next to Highway 1 – and open acoustic windows don’t really help.
TomTom1
K.Brodbeck
12 Jun 2013 20:50
TomTom1 schrieb:
Hello!
Interesting connection – but it’s probably not correct. Heat storage depends on mass. A lot of mass stores a lot of heat, but heat transfer works differently. Try holding a (heavy) metal rod in a campfire .
Tomtom.
However, some experts see this differently! Do some research if you’re interested in the topic. Look up summer heat protection.
TomTom1 schrieb:
Hello!
And vacuum insulation panels tend not to conduct heat, but they also don’t store it.
Tomtom.
Vacuum doesn’t have any mass either, right? I wouldn’t recommend it to anyone anyway.
TomTom1 schrieb:
Hello!
And regarding ventilation: The old apartment was right next to motorway 1 – and open soundproof windows don’t really help .
Tomtom.
Ventilation doesn’t mean keeping the windows open all the time, but rather targeted shock ventilation. During hot periods, this is usually possible at night or early in the morning. I grew up about 100m (330 feet) as the crow flies from a four-lane motorway back then. We were still able to ventilate
Bauqualle
12 Jun 2013 21:09
K.Brodbeck schrieb:
Some experts see this differently!
.. then they are not experts and have no clue ..
K.Brodbeck schrieb:
Glass wool has a low thermal storage capacity, meaning it transfers heat relatively quickly. Cellulose and/or soft fiber boards have a significantly better thermal storage capacity. This means the living space behind them heats up later.
.. wrong .... you should talk to a building physicist
Bauexperte
12 Jun 2013 22:16
Bauqualle schrieb:
.. then they are not professionals and have no clue .... wrong .... you should talk to a building physicist
No, you are wrong ...
[TR="class: heading"]
[TR="class: desc"]
[TD="colspan: 2"]Nominal thermal conductivity value λ ≈ 0.04 W/mK
[TR="class: desc"]
[TD="colspan: 2"]Heat storage capacity S ≈ 16 kJ/m³K (0.45 BTU/ft³°F)
[TR="class: desc"]
[TD="colspan: 2"]Water vapor diffusion resistance factor μ ≈ 1 - 2
[TR="class: desc"]
[TD="colspan: 2"]Specific heat capacity: 830 J/kgK (0.20 BTU/lb°F)
[TR="class: desc"]
[TD="colspan: 2"]Density: 20 kg/m³ (1.25 lb/ft³)
Mineral Wool
Glass wool and stone wool are among the most affordable insulation materials and are therefore widely used. However, their good thermal insulation performance is offset by a much poorer summer heat protection. This is apparently so inadequate that hardly any manufacturer dares to display corresponding data on their website.
The key factor for summer heat protection is the heat storage capacity, meaning the ability to store heat per cubic meter of insulation. This value is the product of the well-known specific heat capacity and the material’s density. The latter varies from product to product and can often only be obtained by direct inquiry. A spot measurement on a package of 50mm (2 inches) thick glass wool mats (WLG040) showed a density of only 15 kg/m³ (0.94 lb/ft³)!
Mineral wool is also sensitive to moisture. Even a small amount of moisture ingress significantly reduces the insulation effect. If mineral wool becomes so wet that the fibers stick together, replacing the insulation is often the only solution.
Since mineral wool cannot store or transport moisture, it is unsuitable for insulating a timber-frame house. For this purpose, insulation materials made from natural fibers are recommended, especially wood fiber insulation boards. Nowadays, approved insulation materials no longer contain fibers harmful to the lungs. Nevertheless, irritating dust is generated during installation, so it is advisable to wear a fine dust mask for protection.
Available forms: insulation mats as boards and rolls as well as loose fill wool.
Source: Ecological Building Material Information System of the Bavarian Chamber of Architects
Not every user here in the forum is “just” a building owner
Regards, Bauexperte
Thermal insulation effect: XXXX0
Summer heat protection: 00000
Water vapor permeability: high
Saruss
12 Jun 2013 22:49
About the physics, in case you're interested:
With materials that have good insulation properties but low heat capacity, the following happens, for example, with solar radiation or significant one-sided heat gain: They become very, very hot (low heat capacity – temperature rises greatly for the same amount of energy). If a low density is added to this (see Bauexperte’s post), the effect is even more pronounced. The amount of energy (important!) transferred through a layer depends not only on thermal conductivity but especially on the temperature gradient between the two sides of the layer. Therefore, with many good insulating materials that have low density and low thermal conductivity, the sun-exposed layer quickly reaches high temperatures (try touching an insulated facade in summer... or better, hold your hand close to it...) – result: a lot of energy is transferred, and the interior also heats up quickly.
A material with high heat capacity not only stores heat energy but also heats up much less. This leads to a small temperature gradient, and less energy is transferred. A simple (thick, monolithic) wall can even delay the energy flow so much (>12 hours) that by the time the energy arrives inside, it is already cooler outside, and the energy flows back outside, causing only very small amounts to reach the interior (often mistakenly labeled as “energy loss” in thermal imaging, although it was free solar energy).
I imagine it’s similar with the roof: the roof tiles receive enormous amounts of energy, and material with higher heat capacity counteracts the heating, creating a much smaller temperature gradient and providing better protection against heat.