ᐅ Buffer tank quickly loses temperature during domestic hot water use

Created on: 22 Dec 2025 16:40
B
Birdies
B
Birdies
22 Dec 2025 16:40
Hello everyone,

We have had a heat pump with a buffer tank "Citrin Solar Heat Pump-SKS 650-1 premium" for almost one and a half years now.

We have been observing the following issue and have been discussing it with the installer for quite some time, who has also involved the manufacturer Citrin. It feels like they are trying to shift the blame to each other, but so far we have not seen a solution.

Effect in WINTER, when the heating is running:
The lower part of the buffer tank is around 30-35°C (86-95°F). All radiators are working properly.

The domestic hot water (DHW) area at the top is heated to 50°C (122°F) starting at 3:30 pm to use photovoltaic electricity if available.
However, we can see and FEEL that the water cools down quite quickly again.

We lose about 15°C (27°F) in the DHW area within a few hours, even without any DHW consumption.
As a result, we have nicely solar-heated water around 3:30/4:00 pm, but by the time you want to shower in the evening, say around 10 pm, the hot water is no longer sufficient.
Not to mention filling a bathtub.

Together with the installer, a test was carried out where all supply and return lines and any other connections to the tank, circulation, solar, etc. were closed.
The DHW was preheated to temperature beforehand.
No DHW was drawn during the entire recording period!

Diagram with temperature progression and hot water preparation as bar and line graph


(The three very thin orange bars are only markers, not DHW heating!)

For comparison, in SUMMER:
The entire tank is heated to 55°C (131°F) by the solar thermal system on the roof, both top and bottom.
Heat loss from evening (sunset) until the next midday, when the sun shines on the solar thermal panels again, is only about 3°C (5°F).
Even if there is no sun for a full day after that, the temperature loss of about 8°C (14°F) over TWO days is still reasonable.

My question:
Is such a drastic heat loss of the buffer tank normal and acceptable, or is there a fault here?
Would it make sense to use the tank only for DHW and connect the heating circuit directly to the heat pump? This was a suggestion already discussed with the installer. (My concerns are possibly an increased number of compressor starts, but the installer believes this would not happen because the system "modulates" and instead of on/off would run continuously at a lower required power.)
With this idea, there would be NO buffer in the heating circuit.

Viessmann Vitocal 250 A

The house currently has two heating circuits, which work well with the current settings:
  • Underfloor heating in living/dining area ~40 sqm (heating curve level 4 slope 0.2)
  • Radiators ~120 sqm (heating curve level 5 slope 0.4)
Both circuits are limited to a maximum flow temperature of 30°C (86°F).

Currently, the system is connected/set up as follows:

Technical heating system with heat pump, buffer tank, and piping diagram.


There is a meeting with the installer in early January, and until then I would like to understand whether the proposed solutions make sense, could cause issues, and so on.
They have already stated themselves that such a temperature loss is not normal and have reported it as a defect.
J
Jesse Custer
22 Dec 2025 17:01
Allow me to point out: this system is not suitable for heat pumps.

The fact that the water cools down quickly in winter is completely understandable – there is no real separation between heating and domestic hot water. This is not a mistake; it is simply physics.

In summer, with solar energy, it works fine since the heating is not running and does not extract any heat.

But what you need is not an indirect hot water cylinder, but a heat pump-specific model... as even stated in their description...
N
nordanney
22 Dec 2025 17:46
Therefore, the storage tank should only be used for hot water, and the heat pump should be connected directly to the underfloor heating. Anything else causes hydraulic issues.
P
Peter_H_
22 Dec 2025 18:59
I have to agree with the previous speaker; it seems to be a corrugated tube storage tank, where the corrugated tube with the potable water extends through a significant part of the buffer and thus takes on the exact temperature of the buffer. Check how the temperature changes within the buffer. It’s probably the same as the potable water. If you really want to continue using a buffer, a stratified storage tank with a fresh water station would be appropriate. However, as mentioned before, this is actually not very practical. A dedicated domestic hot water tank with the underfloor heating connected directly to the heat source would likely be better.
P
Peter_H_
22 Dec 2025 19:16
Unfortunately, I can no longer edit. I just noticed that the tank probably has a separating baffle. Maybe check where the heating system draws the hot water from. It’s possible that the heating cools the upper volume and, with it, the potable water as well.
J
Jesse Custer
22 Dec 2025 19:29
Peter_H_ schrieb:

Unfortunately, I can no longer edit. I just noticed that the storage tank seems to have a stratification plate. Maybe check where the heating system draws the hot water from. Perhaps the heating system is cooling the upper volume, and therefore also the potable water.


It doesn’t have one right now – the solar buffer tank doesn’t, the heat pump one does...