rennschnecke26 Mar 2022 16:09Hello,
I am currently replacing all switches and sockets. So far, this hasn’t been a problem and everything is working smoothly.
Only the switch in the bathroom is puzzling me.
Attached are photos of the old switch and the new one.
L is clear. However, the new switch does not have an N like the old one.
L is also the live wire, which I have verified.
No matter whether I connect the blue or brown wire on the right or left, when I operate the switch, the circuit breaker trips.
Does anyone have any advice?

I am currently replacing all switches and sockets. So far, this hasn’t been a problem and everything is working smoothly.
Only the switch in the bathroom is puzzling me.
Attached are photos of the old switch and the new one.
L is clear. However, the new switch does not have an N like the old one.
L is also the live wire, which I have verified.
No matter whether I connect the blue or brown wire on the right or left, when I operate the switch, the circuit breaker trips.
Does anyone have any advice?
R
rennschnecke26 Mar 2022 16:39Edit:
I have this one from Kopp:
PARIS – universal switch (on/off/changeover) with lighting, color: matte black
PARIS – indicator switch, color: matte black
I have this one from Kopp:
PARIS – universal switch (on/off/changeover) with lighting, color: matte black
PARIS – indicator switch, color: matte black
R
rennschnecke26 Mar 2022 23:25A two-way switch controls a light from two different switches. This is not the case here. This is a standard single-pole switch, meaning one switch controls one light.
rennschnecke schrieb:
So far, that is not a problem and works smoothly. A miracle considering this statement:
rennschnecke schrieb:
A two-way switch controls a light from two switches. That is not the case here. This is a standard switch, meaning one switch controls one light. rennschnecke schrieb:
Edit:
I have this one from Kopp:
PARIS – Universal switch (on/off/change) with indicator light, color: matte black
Or is this the wrong one and I need this one?
PARIS – Universal switch (on/off/change) with indicator light, color: matte black You don’t have either of those. You have the 5036 from Kopp. Get one of the other two and just reconnect it, then it should work. The only difference is the indicator light, which is red or white.
B
barfly66627 Mar 2022 09:18Do you always connect both blue and brown wires together on the left or right side?
A short circuit between L and N will obviously trip the breaker…
Leave the blue (N) wire out of the switch.
A short circuit between L and N will obviously trip the breaker…
Leave the blue (N) wire out of the switch.