ᐅ Concrete slab – vapor barrier against rising moisture

Created on: 30 Sep 2019 13:58
A
AnSe2019
Hello everyone,
in most constructions, you can see that a "membrane" (I can’t recall the exact technical term right now) is placed between the concrete slab and the masonry to prevent rising dampness.
In our shell construction, from what I could observe, this seems to have been omitted. Before I discuss this with the site manager, I wanted to ask for your collective knowledge to find out if this is normal, what the possible reasons might be, or other relevant information. Maybe my concerns will be resolved already.
I’ve attached a photo. If it had been done, you would see it, right?
Best regards
A
AnSe2019
30 Sep 2019 18:59
Excerpt from the construction specification:
"The foundation slab will be constructed as a reinforced concrete base according to the structural engineer’s design and sealed on the top surface. An 8 cm (3 inch) insulation layer will be installed beneath the foundation slab. Installation of a grounding flat steel strip."

If the black material is a membrane, then it should be placed beneath the slab, not sealed on the top surface. Or am I misunderstanding?
D
danixf
30 Sep 2019 19:18
Why below? Isn’t it actually placed on top of the slab?
Don’t you have a schedule for the different trades?
I assume the waterproofing membrane is still to be installed. In our case, it was applied shortly before the window installation. The joint is coated with bitumen, Remmers 2K waterproofing or a similar product.
AnSe2019 schrieb:

Is the membrane really installed between the ground and the slab?


Between which ground? Your future floor? Yes, where else would it go?

Edit: Here is a photo from our start.

Construction site with wheelbarrow in front of foundation components and construction boards
N
Nordlys
30 Sep 2019 19:31
Exactly, that's how it is. And the floor will still get a bituminous membrane made from roofing felt.
A
AnSe2019
30 Sep 2019 21:38
Okay. I think I had mistaken a dark spot for a membrane. Specifically, the one on the right in the photo (under the slab). But now I see that something is also sticking out on the left between the slab and the wall. That makes me feel reassured for now. Thanks for your sharp eyes and professional expertise.

Unfinished building: two red brick columns with white base, door opening, concrete floor, soil in front.
G
guckuck2
30 Sep 2019 21:43
Correct. Once the shell of the building is complete, the roofer usually comes to fully cover the ground floor with waterproofing membrane.
M
Mottenhausen
1 Oct 2019 12:18
Even better, your foundation slab is already sealed from below and therefore dry because of the Styrodur
AnSe2019 schrieb:

An 8cm (3 inches) layer of insulation is installed below the foundation slab

and similar products are waterproof by design. Additionally, there is probably a membrane underneath the slab insulation as well. So everything is fine. As long as no mistakes are made during the exterior plastering, moisture should stay outside.