ᐅ Experiences with Ground Source Heat Pumps

Created on: 23 Oct 2015 21:40
S
Saruss
Hello,
here I would like to share some experiences and data regarding my brine heat pump and deep drilling, based in part on the expert’s "questionnaire":

a) What is the soil composition on your property?
Up to 3m (10 feet) silty, fine sandy, clayey soil
Up to 4m (13 feet) slope debris, rock fragments
Then bedrock (mainly limestone)

b) How deep was the drilling?
Drilled twice to a depth of 72m (236 feet)

c) How much did the drilling cost?
€10,400 including double U-probes DN25
Grouting material with 2.0 W/mK thermal conductivity
Permitting process (building permit / planning permission)
Pressure-tight house entry at the basement and underground routing of supply lines (about 25m (82 feet))
Filling/draining equipment, filling, pressure testing, etc. (all inclusive)

d) How much did the system cost?
System: Tecalor TTc 05 with heating output at B0/W35 of 5.8 kW and coefficient of performance (COP) of 4.8
Cost: €9,800

e) Were there any difficulties during installation, if so, what kind?
Because the water used to flush out the drilled material during drilling seeped away, a "small compressor" was needed to blow it out with air. However, it had to be placed on a neighbor’s property who had not yet started building. The machine was the size and approximate weight of a 20-ton truck but was off-road capable. This caused a 2-day delay because the compressor first had to be transported to our site. No additional costs were charged.

f) How is the daily operation?
"Like a refrigerator." Once the parameters on the heating system are correctly set, the only thing that should be done is occasionally reading the information/data such as operating hours and source temperature. Otherwise, it runs "on its own," just like any heating system. When the door is closed, the unit is virtually inaudible. Very discreet since, apart from the cabinet in the utility room, nothing else is visible (all brine pipes are underground).

e) What are the operating costs for which living area?
Currently, a living area of 180sqm (1937 sqft) is heated, plus an additional 65sqm (700 sqft) of cellar space within the insulated thermal envelope (these rooms are around 15-16°C (59-61°F) on the coldest days). From September 2014 to September 2015, 2,000 kWh of electricity was consumed for heating and hot water (2 adults, 1 baby, 1 toddler). The house is a KfW-70 standard building according to the 2009 energy saving regulations, which already met the required technical standards before the central ventilation system with enthalpy heat exchanger was installed (we decided to add this after the initial applications).

f) to be continued ....

Note regarding the comparison of the coefficient of performance (COP):
Since optimizing the heating curve and settings at the end of last year, the system has had a COP of about 5.5. Operating hours are around 1200; the deep borehole was drilled approximately 20% deeper than initially recommended by the companies, at our own request.
W
Wickie
20 Mar 2018 13:00
I quickly checked as well:

2 x 80 meters (260 feet), soil class 1-5,
7.7 kW heat extraction capacity,
total gross cost 9,400
(drilling net cost just under 6,700, probe connection net cost 1,250).
Drilling was done last month
T
toxicmolotof
20 Mar 2018 13:07
This clearly shows how quickly different power outputs drive the price up. At some point, you have to (rightly) ask yourself whether it is still worth it.
T
toxicmolotof
20 Mar 2018 13:11
860 euros/kW to 1,220 euros/kW

That’s a lean 40% increase, which is not just due to the drilling company but also because of the ground conditions.
B
Bookstar
20 Mar 2018 13:22
toxicmolotow schrieb:
Okay, I just checked...

105 m (3x35) in water protection zone IIIa, soil class 1-5, 6,200 W heat extraction capacity, completely pre-pressed with connection all the way to the house, permit/planning permission, etc., basically fully finished, all inclusive.

Gross price €5,350.19 (net €4,495.96) plus €250 city tax.
(February 2015)
The price is insane. Today, I got a quote from a work colleague for a 7 kW system, all inclusive, gross €14,900.

Now I'll just accept that I live in a “ridiculously” expensive area.
A
Alex85
20 Mar 2018 14:59
Regarding the experiences, bookstar, I can understand you.
I would never pay €14,900 for drilling. That’s not something you can just brush off.

toxic, with so many short drilling jobs, your price was really great. Your soil seems to be in good condition, which I would also like...
D
denz.
20 Mar 2018 17:06
Alex85 schrieb:
For a 6 kW heating unit, you need about 4.6 kW extraction capacity

Do I understand this correctly? If the heating load calculation results in 6 kW, the borehole is designed for only 4.6 kW? I had assumed that the borehole would be made for 6 kW or even slightly more, around 6.5 kW.

Regards
denz